Steam boiler
Snowmelt
Snowmelt Member Posts: 1,428
I took one apart Friday, waiting for customer to have money for new boiler. My supply house boiler guy took a section , dropped it on the ground and it broke in two, he thinks it was dried firered.
  • STEVEusaPA
    Looks like good ole..rotted out. Can't seem to click on the pic to zoom in.
    Jamie Hall Member Posts: 26,183
    Could be just rotted. Could also be... brittle failure. Keep in mind that cast iron is brittle, not ductile (why bashing a cast elbow can break it off so you can replace it!) and perhaps your supply house guy dropped it far enough for the shock to break it. Impossible to be sure unless you can study the fracture surface closely.
  • Snowmelt
    He dropped a few sections and didn’t break, he dropped the 4th section at same height and it broke, then you can see the fresh metal vs the metal that was all rusted. If that makes any sense?
    Just depends on exactly how it hit. Possibly with latent flaws in the casting. Plink!
    ethicalpaul Member Posts: 7,762
    Just for clarity...what's the question? :)
  • Snowmelt
    Question is, where the hell all that soot come from, and if I never saw water on the ground that doesn’t mean it didn’t have a leak
    I can't tell from the photo, but how much of that pile is soot vs rust I wonder?
  • ChrisJ
    ChrisJ Member Posts: 16,851
    Why would dry firing it make it brittle?
    I would expect the typical conditions to anneal cast iron if anything. I don't think it was dry fired based on the evidence provided.
    Cast iron is brittle by nature.
    Quite correct on all counts, @ChrisJ !
  • Snowmelt
    I have another pic of a section I saved
  • gennady
    gennady Member Posts: 840
    Dry fire would damage all sections.
  • ChrisJ
    edited September 2019
    Hi Gennady,
    What kind of damage is usually seen on a dry fired boiler?
  • gennady
  • retiredguy
    retiredguy Member Posts: 1,051
    Dry fire a cast iron boiler long enough and the sections will melt. Actually, firing any boiler, steel or cast iron and they will melt. I have seen it happen many times.
