water flow stops,when bleeding system
Any suggestions ?
Thank You.
Well water? If so it might take time to pressurize the wells expansion tank. At times I've bypassed the PRV and hooked up a hose directly from a cold water valve to the boiler drain valve.0
No,not well water,just regular street main.0
the PRV i installed brand new.Yes,I'm watching pressure on the boiler.When it reaches 20-25 psi,I close return valve and open drain valve.Water goes down nice and almost stops,till next drainage.0
"I have 2 loops upstairs,but only 1 circulating pump. There are no bleeders on baseboards."
Is it a zone valve system? If so are you opening each zone manually to allow flow to each of the 2 loops?0 -
yes,exactly.0
Sounds like you have a restriction somewhere in the fill system. Back check, PRV etc.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
looks like water flow is limited by something in system after boiler.0
Just a thought. Did you flush out the water feed line before connecting to the BFP and PRV? There's often a nice wad of crust jammed in there if the domestic isn't filtered. Mmmm.
When you wrote "rebuilt all inline valves", explain please. Can you post some pics of the work?0 -
I mean rebuilt,that's returned valves,drain valves,boiler drain valve: replaced packing and washers.Replaced boiler PRV,air vent,ET.0
Ah... hold the phone here. Water will only flow if there is a pressure difference. So I'm a little confused. If the drain is open and the feed is open, water should flow -- even if there is a restriction, at least some flow should take place. How is pressurized water getting into your system when the drain is open? How is it finding its way to the drain?frimi said:the PRV i installed brand new.Yes,I'm watching pressure on the boiler.When it reaches 20-25 psi,I close return valve and open drain valve.Water goes down nice and almost stops,till next drainage.
That's what problem is.Drain valve is opened, feed valve is opened on manual (full pressure from street),but just a little bit of water 's coming out (i've been waiting for 10+ minutes)0
maybe post some pictures,
one wide shot of the whole boiler area,
where you're draining,
the fill,
and the control valves to each zone,known to beat dead horses0 -
OK. Something -- somewhere in your system -- is closed or nearly so. If it's not a stray valve somewhere, or a faulty pressure regulating valve on the feed line, first look for an overlooked valve. Don't assume anything!frimi said:That's what problem is.Drain valve is opened, feed valve is opened on manual (full pressure from street),but just a little bit of water 's coming out (i've been waiting for 10+ minutes)
And don't try to run the boiler or circulator until you find and fix the problem.Br. Jamie, osb
I can't push water in a wrong way,as I didn't change anything in piping,just serviced some valves.Before that everything worked as supposed to.0
can you break a union after the feeder and confirm it does fast fill, or feed at all?known to beat dead horses0
I have a pressure gauge installed in system,by the ET.When feeding valve is set on auto,the pressure stops at about 15 psi (my base boards on 3rd floor,boiler in the basement).When feeding valve is on manual(full street pressure),the gauge slowly goes up,and I start bleeding,when it reaches 25psi(less than 30psi,not to trigger PRV).That's why I assume the feeding valve works properly.0
Did the innards of one of the valve you took apart and rebuilt stay inside and plug it up or maybe the new washer came loose and wedged in the seat?0
Take them all apart and service them again. Something went wrong with one of them. General rule: if it worked before you worked on it, and doesn't work now, the problem is something you did when you worked on it.frimi said:I can't push water in a wrong way,as I didn't change anything in piping,just serviced some valves.Before that everything worked as supposed to.
i understand that,but why when I start bleeding water goes nice,full stream,after few seconds's slowing down and stops,almost. If that's something wrong with valves,then it would be right away,when start bleeding,not after say 30-40 seconds.0
there are some pics I took from my system
Might be a check that is integral to the circulator as well, so it might only pass in the direction of normal flow.0
when your draining,
you have the fast fill engaged? full street pressure, correct?known to beat dead horses0 -
Are you purging one loop at a time? I'm asking because of the wye hose adapter.
Its possible the PRV is not set to 12 psi so even with the lever up, its still feeds slow. Have you tried adjusting the PRV?0 -
Yes,full street pressure, one at a time.0
well then what Jaimie said,
take it back apart and see where you did what wrong,
there's a valve blocked or closed there somewhere.known to beat dead horses0 -
When you said you replaced the prv, did you mean pressure reducing or relief valve? Also, when you purge, close both red handles on the return piping, and using a single hose , individually open the drains above , and see if the flow is good from either with 20 to 25 lbs pressure. If it isn't, open the red handle below and see if it improves.0
Like @Jamie Hall said, the problem lies in the work that was done. I would start with the "rebuilt all inline valves" part. Occam's Razor.1
going away from home for 2 weeks; will continue,when back.0
Some debris is probably caught in the piping. When you bleed the system water "goes nice" as you say. Then after a few seconds it slows down and stops.frimi said:i understand that,but why when I start bleeding water goes nice,full stream,after few seconds's slowing down and stops,almost. If that's something wrong with valves,then it would be right away,when start bleeding,not after say 30-40 seconds.
Possible debris is floating in the piping causing a obstruction while bleeding. It's time to take things apart and look.1 -
I'm back and finally found the culprit. The pressure reducing valve,the only one I didn't touch had debris in inlet and let very little water to flow,even when on manual(street pressure).Still system shown high pressure,but when accumulating water was drained it stopped water flow almost completely(had to wait 5-10 minutes to fill system again).
Now I have another question : I bought new pressure reducing valve Watts model 1156F,which preset to 15 psi. Should I now precharge my expansion tank to 15 psi also,or to leave it to factory charge 12 psi ? Thanks everybody for help.0 -
The pre charge and factory charge are nominal. In your case you can leave the two set pressures as they are.0
um,Intplm. said:. . . In your case you can leave the two set pressures as they are.
you sure about this?
pretty sure the expansion tank should be set to match the 15# fill valve setting,
or we use up all that expansion on first fill,
pros chime in please, , ,known to beat dead horses2 -
But you have to know how much water is in the tank when you set the charge pressure, right?0
the tank must be either taken off the system, or isolated and drained to zero water pressure,
, , , so no water in the tank.known to beat dead horses0 -