Munchkin Replacement
Dan Foley
Member Posts: 1,268
We replaced this 15 year old Munchkin boiler yesterday. It was at the far end of a 42” crawl space. At least it had a rat slab. We laid down a foam walkway to crawl on but it was still no fun.
1
We went back with an NTI LX because it is short, floor mounted and the controls are accessed through the front.
We cleaned up the Pex piping as best we could. The 45 gal. Indirect was replaced with a 65 gal NTI. The owners complained of running out if DHW. This was the biggest tank that would fit in a tight closet.3 -
The existing DHW tank did not have a T&P. Someone installed a black cap instead. It had pinholes and was leaking. There was not much metal left when we removed it. It was almost ready to let go.0
@Dan Foley Nice looking job considering what you inherited You needed 4 foot tall installersRay Wohlfarth
Boiler Lessons1 -
Grand improvement.
Who said that lipstick doesn't work.
We have all known home owners who do not want any equipment visible or do not want to lose closet space. Then in a few years they cry tears because no one wants to work on their stuff.
They should be grateful to you for what you did....a good tip is in order I think.....bill accordingly.
Isn't there any code that requires equipment as such to have a minimum ceiling height? Circuit breaker boxes need 6 or 6 1/2 feet of ceiling height. I learned this the hard way BTW.2 -
well a black cap with pinholes is kind of like a T&P . . . no?Dan Foley said:The existing DHW tank did not have a T&P. Someone installed a black cap instead. It had pinholes and was leaking. There was not much metal left when we removed it. It was almost ready to let go.
3 -
nice indeed. gotta love crawl spaces. and cpvc better than previous by a long shot albeit although still theoretically non-conforming by stack temp if you are running indirect hot water which is looking for 180 degree boiler water temp and has relatively hot return.
when i go back to these jobs, if it is remotely possible, i'm switching to on demand condensing hot water to get the stack temps down in the boiler and in the water heater and working with emitters for as low a design temp as possible.
I've had incredibly trouble free operation with the non-condensing on demands in place for like 15 years without trouble. Don't know if the condensing units will last as long but I'm stoked with stack temps all around.
not criticizing, you play the hand you are dealt and left it way better than it was.
I have found that the System 636 has the DWV style 90 in CPVC. It isn't really a sweep el as they claim, but it is by comparison to those those blunt standard CPVC turns - which i don't even like for pipe friction with fluid flow - although with the higher unit in the crawl space you might have been limited. i wish they would make the DWV pattern 45s in CPVC as well.
Definitely like the crawl path! Save the knees for the next job.
Dan, a dual check, no vent accepted on the boiler fill?
Certainly solves the dripping issue if code accepts it.Bob "hot rod" Rohr
Hi HR,
Technically thus would not pass code. 1. It is unlikely the inspector is going to crawl 30’ across this crawl space to check. 2. There is no floor drain. No one will notice the backflow is leaking until it floods the space.0