Oxygen barrier tubing when no ferrous material in system All components stainless or brass
mattlapp
mattlapp Member Posts: 1
if you install a radiant system and have a high efficient Stainless boiler, with Stainless circulator, is there any need to install oxygen barrier tubing ?
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,511
    No. But, someday in the future, you may want to have option of cast iron....
  • Zman
    Zman Member Posts: 7,611
    What you described is the work around when the wrong tubing is installed. It works fairly well.
    The correct tubing is not very expensive and is really the way to go. Your water chemistry will be more stable and you won't need to worry about the little parts which may be prone to corrosion.
    Albert Einstein
    Rich_49Canuckerdelta T
    hot_rod Member Posts: 26,602
    Expansion tank and any connections also need to be non-ferrous, of course. I think it would need to be a large tube job before the $$ worked out over barrier pex, Pert, etc?
    Rich_49
  • heathead
    heathead Member Posts: 241
    Better Read you boiler warranty. Most Read that O2 barrier Tubing is required or you need a heat exchanger. Even some that have a Stainless Steel heat exchanger. Just a thought.