boiler firing rate for efficiency

Options
zett
zett Member Posts: 4
I'm just not seeing the forest for the trees and could use the wisdom of the wall...

I'm wondering how to set the firing rate.

I'm the facility manager at a small school and have a Peerless Cast Iron boiler that has a potentiometer on the burner. I can set the burner to high or low fire or anything in between. I've set it so the water in the glass is not bouncing wildly or that there is no water dropping into the steam side of the glass. This is as high as I dare go. This will get the pressure to 1.5 pounds in about 3 to 4 minutes. If I set it lower, I assume I will use less gas, but it takes 2 or 3 times as long to reach the cut out pressure. Either will keep the building warm just fine.

My question is which setting is more efficient in the long run?
Does the higher fire use more gas or the longer low fire?

I'm attaching a photo of the firing rate per hour (i've attached a sensor to the gas valve, so it's actually showing the number of times the valve has opened.) You can see how the firing rate was lowered after 1pm.

Any help appreciated,
John

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    Options
    What is the make of the burner? Normally the burner would be set up with combustion testing equipment to make sure the exhaust is within certain parameters for efficiency.
    Ideally, the capacity of all the radiators should match the steam generation of the boiler, and maybe the burner could thus be adjusted to make this happen.
    1.5 psi should normally be the upper limit on pressure for the system, which would be limited by the pressuretrol.—NBC
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,544
    Options
    If the burner has a potentiometer then the boiler also has (or should have) a Honeywell L91A or b modulating pressure controller on it. This is a 3 wire control with the connections marked R,W,B this is what we call a "full modulation" burner. Power Flame? Webster? Industrial Combustion?

    When adjusted correctly this control will modulate the burner to maintain the steam pressure you want without having to adjust the manual potentiometer.

    Depending on the burner you have the wiring is a little different. Some burners have a manual-auto switch and you can select between the pressure control or the potentiometer to modulate the burner.

    If the burner on high fire bounces the water level too much then you have 1 of two problems:

    1. The boiler water is dirty and needs skimming
    2. or the burner isn't set up right and could be over firing

    I would set the steam pressure high limit or operating pressure control to 5 psi. Then use the modulating control to modulate the burner at 1 1/2-2 psi.

    This will reduce burner cycling and maintain the pressure you want
    ttekushan_3
  • zett
    zett Member Posts: 4
    Options
    The burner is a Gordon-Piatt and I believe we do have a Honeywell L91 modulating pressure controller.

    The burner may be overfiring as the water is not dirty.

    I did adjust the operating pressure control to 5lb with cutout at 1lb and put the burner on automatic with the potentiometer at low setting.

    The pressure seems to be holding at 1.5 now!
    Looking forward to longer cycles now.
    Any other suggestions?

    Thanks!











  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,544
    Options
    Sounds like it's working. You can get a bouncing water level even if the water looks clean it could have oil etc on the surface but if it isn't surging leave it be

    Looks like you have a manual auto switch on the panel next to the pot.

    Gordon Piatt is out of business. If you need burner parts there is a company in Ohio (I think) that has some parts. You can Google it.
  • zett
    zett Member Posts: 4
    Options
    Appreciate the tips!
  • Dave in QCA
    Dave in QCA Member Posts: 1,785
    Options
    Yes. What EBEBRATT-Ed said. I had skipped some of the replies, was going to type a detailed answer, but looking back, I see that Ed already covered it. Only thing I would add, is that proper adjustment of the air/gas mixture for proper efficiency is done at both ends of the modulation range. I should be covered in your burner manual.
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    Options
    If you need Gordon Piatt parts, call Cici Boiler Boiler Rooms and ask for Chris Dasher. Tell him Mike Sheppard referred you.

    Here is their website:
    https://gordonpiattparts.com

    That burner has a manual/auto switch. It should be set to auto. The modulating pressuretrol should be set lower than your operating control and will automatically modulate the boiler between low and high fire. In auto mode on that burner, the potentiometer can also be used to limit high fire, down to a maximum of 50%. This helps during low demand times of the year. I believe they have writing there around the manual/auto switch that explains this.
    Never stop learning.
    ttekushan_3
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    Options
    Generally you get a little less efficiency on low fire, with cast iron boilers but on variable induced draft, it’s probably not as big difference. I think the reason is less infrared transfer from the smaller flames.

    Combustion analysis would confirm this. And as mentioned,d important that it’s tuned on both ends, and they might check it in the middle too and need ot make sure any mechanical linkage doesn’t have a lot of slop.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,544
    Options
    In general the flame on low fire may be slightly less efficient than on high fire but the stack temperature is also reduced on low fire so it balances out
    Dave in QCA
  • ethicalpaul
    ethicalpaul Member Posts: 5,704
    Options
    Plus low fire by definition uses less fuel so I never understand why people get concerned about a lower efficiency number during down firing.
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
    mikeg2015
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    Options
    If does use more fuel if it runs longer. If you downfire 50% and it loses efficiency, then it has to run >2x longer to produce the same BTU’s.

    A 200k boiler @ 80% efficiency delivery 160k per hour. If heat loss is 100k, it will run 37.5 minutes per hours and consume 1.25 Therms. if downfired to 140k, if effeciency is 78%, It runs for 55 minutes per hours and consumes 1.28 Therms. However, standby time is only 5 minutes vs. 23 minutes.

    That being said, there are some savings to reducing standby losses due to longer run times. But that depends on if the boiler is adjacent to the conditioned space. But in this case, I’d suspect if might be a wash, so the comfort of longer run times presents and advantage. On a 1 pipe steam system you reduce the volume of oxygen ladened air being drawn in and out.
    ethicalpaul
  • Dave in QCA
    Dave in QCA Member Posts: 1,785
    Options
    Don't forget that longer runs also reduce the starts and stops. This will reduce the number of prepurge and postpurge cycles which fan force a chunk of heat right up the chimney.
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
    ttekushan_3
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,544
    Options
    And down firing also always lowers the stack temperature (is has to) which always raises the efficiency as long as the Co2& 02 #s don't fall off the table
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    Options
    Don’t forget jacket losses. Jacket losses stay the same whether it’s at low fire or high fire.

    https://heatinghelp.com/systems-help-center/are-modulating-burners-really-worthwhile/
    Never stop learning.
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,215
    edited March 2019
    Options
    Jacket losses are nearly constant for most boilers in the mid season. I've seen several organizations say that running at high fire is much more efficient because the jacket losses are much higher at low fire. They base this on calculations that assume that as soon as the boiler shuts off, it goes instantly cold.....They have never actually seen a boiler operate.
    Now losses from the draft hood into a room on boilers with stack dampers are a different story.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
    ethicalpaulttekushan_3
  • ethicalpaul
    ethicalpaul Member Posts: 5,704
    Options
    mikeg2015 said:

    If does use more fuel if it runs longer. If you downfire 50% and it loses efficiency, then it has to run >2x longer to produce the same BTU’s.

    A 200k boiler @ 80% efficiency delivery 160k per hour. If heat loss is 100k, it will run 37.5 minutes per hours and consume 1.25 Therms. if downfired to 140k, if effeciency is 78%, It runs for 55 minutes per hours and consumes 1.28 Therms. However, standby time is only 5 minutes vs. 23 minutes.

    That being said, there are some savings to reducing standby losses due to longer run times. But that depends on if the boiler is adjacent to the conditioned space. But in this case, I’d suspect if might be a wash, so the comfort of longer run times presents and advantage. On a 1 pipe steam system you reduce the volume of oxygen ladened air being drawn in and out.

    Thanks for your nice reply. My comment came from a place of thinking where the boiler was oversized and the down firing would be sought as a relief for some of the issues that can cause--I would never advocate it just on its own.
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    Options

    And down firing also always lowers the stack temperature (is has to) which always raises the efficiency as long as the Co2& 02 #s don't fall off the table

    With and atmospheric, on low fire you get more excess air, so stack temp is lower, but O2 goes up because secondary air does not reduce proportionally. Ultimately, air velocity tends to stay similar due to convection. Air mixing in the tubes does stay constant, so air/fuel ratio is probably nearly the same I’d expect.

    If you could drop the steam temp or in a hot water boiler, the water temp, the draft could drop slightly and you might gain economy or at least maintain it.
  • Leonard
    Leonard Member Posts: 903
    edited March 2019
    Options
    Just for comparison in summer my 60 year old cast iron uses ~ .9 gallon of oil per day to stay hot to make DHW ( DHW coil in water jacket). Nossel is downsized to 1.1 GPH

    No motorized exhaust dampers

    2 old people, two warm/hot 10 minute showers per day, 3GPM
  • zett
    zett Member Posts: 4
    Options
    Thanks for all the info!
    I will definitely get a combustion analysis and have it tuned on both ends. I'm feeling like I'm finally getting a handle on this.

    We have a Tekmar and it is doing it's job.
    I am including a spreadsheet of the other day.

    As the outdoor temps rise, the boiler is running at 4 oz for longer cycles, the rads are warm, not hot and the classrooms are just fine.

    We have a building (1913) with single pipe and a 1923 wing with 2 pipe, both heated with same boiler. The boiler was downsized when it was installed in 2000. the engineer did not do a heatloss, but counted rads. 40,000 sq ft, 2 floors with longest runs about 150 feet.
    ttekushan_3