Inherited Copper Pipes
AjhDr0p
Member Posts: 3
Hi all, I just purchased my first home and am going through my first winter. I've dealt with a self-inflicted flooded boiler, and some annoying water hammer. Next on my list is quieting down the air vents from gurgling and spitting (albeit, just a little), but at least my home is warm. The house was redone before I moved in, and I noticed that copper piping was used by the boiler. I've read Dan's book (We got steam heat!) and know that this is not the correct material. Does anyone have any insights into how long the copper may last, and is it worth it to try replacing immediately?
The question is, is it improperly piped? Post up a couple pics of the boiler piping. Copper is not recommended as the expansion rates are much different then the boilers cast iron, from all the expansion and contraction over the years the soldered joints could come loose and create leaks. If they utilized both risers in copper it can then create stresses on the boiler sections causing them to fail and leak.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Thanks for the quick reply Dave. Attached are some pictures.
The good news is that it's threaded pipe on the steam lines from the boiler. The bad news is that it's almost all wrong... I'm not a bit surprised that you have some gurgling and spitting vents.Br. Jamie, osb
I'll take that good news (and wish it stopped there). Any additional info on what's wrong with the setup, or how to stop the gurgling and spitting from the vents? I've been trying to troubleshoot (the vents all seem to work, although I've just invested in a few more (Varivalve 925005-00 Adjustable Angle Vent Valve), radiators are all pitched, the water is crystal clear (except when going through a cycle).0
Other than the water supply pipes , I don't see any copper on the STEAM related pipes.
Hard to see, but are the elbows and Tees the copper you are talking about?0 -
The near boiler piping couldn't be better set up to get wet steam into your system. That's the most likely reason you hear gurgling. It needs to be repiped to at least what the install manual recommends. You can do it yourself, if you're feeling up for itYou can have it good, fast or cheap. Pick two0
- 87.1K THE MAIN WALL
- 58 Biomass
- 117 Chimneys & Flues
- 111 Geothermal
- 163 Indoor-Air Quality
- 72 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 55 Water Quality
