Protection of power supply
mayurilahane
Member Posts: 2
As in power surge? On the boilers that have circuit boards I install a surge suppressor where it plugs in....0
It was not practical to install a surge protector where my boiler plugs in because it does not plug in; it is wired in. I had a whole-house surge protector installed in my main distribution panel. Stuff like my computers, stereo, etc., do get supplementary power strips or UPS boxes.
I believe the question was protecting against reverse voltage.
But if you really mean that, you need to provide some additional information of what your wiring looks like and why you would need to prevent "reverse voltage".0 -
Your question needs some clarification.
Odd question , most power supplies use 120VAC ( that is a sine wave so polarity of hot and neutral switch 60 times a second ( 60 hz)
Other power supplys run on DC........ Do you want to protect your power supply from wrong DC polarity power going INTO it ( on it's input) .
OR do you really mean you want to protect a DC LOAD from reverse polarity that a power supply might provide0 -
I can't think of better protection than the 400 series ICM ( within common folk price range ).
https://icmcontrols.com/products?c=LINE%20VOLTAGE%20-%20SINGLE%20PHASE%20MONITORhvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
I consider surge protection a necessary add to any home boiler (and many other things).
The problem is that the small low cost ones are based on electroic devices that loose life every surge they see... and are often dead in 5-10 years; and they do not tell you that they can no longer protect against any surge (must less a large one).
Transformer based surge protectors provide basic surge protection that lasts for the life of the transformer (50-100 years). Electronics can be added to make them better... and those electronics are after the transformer and never see most of the surge... and tend to last an estimated 20-30 years (and perhaps longer). Of course, tranformers are not cheap and they take some room.
I have a hardwired "FF1-20W-120 - #002-00072" from Zero-Surge installed in my power supply wiring to my Vitodens 200 Boiler.
https://zerosurge.com/commercial-solutions/
Some people go for the plug in version:
https://zerosurge.com/plug-in-products-solutions/
I have a variety of both the "2R" 15 W and one 20 W version (for my treadmill) scattered throughout my house.
For me its peace of mind an knowing that my boiler will never see a surge (and given the cost of the circuit boards....).
So above is step 1.
Another possibility is to get a pure sine wave output double conversion uninterruptible power supply. This first converts all incoming voltage to DC, then it converts the DC to a pure sine wave output (no noise) and provides run time if the power goes out.
In my case I acquired some used pure sine wave double conversion industrial UPS's for my house. I have 4 added battery packs for the 20W version for my boiler - which should provide a range of 2 days to almost a week or added run time in the event of a power outage depending on the condition of the batteries.
I have found that the batteries need to be changed every 4-5 years. They are due again this year before heating season as the internal monitoring system tells me that the batteries are degrading (I'm not so worried this summer).
Hope that helps,
Perry0 -
Have you tested the run time of the UPS? I found that when powering small loads off a UPS, the inefficiency of the inverter used far more power than the load itself.0
Not fully, it only had to run about 1.5 days once. The battery level indicators indicated at least 50% more battery life left at that point.
The technical literature does indicate how much power its conversion and control unit consumes. Its available storage rating is what is available with fully charged new batteries above internal usage.0 -
I suspect that this post is an ad for this school https://online.crbtech.in/courses/online-electrical-design-training-course/
I would think that wiring it correctly would solve the issue..."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0