Do I need a mixing valve?
WillTheGreat
WillTheGreat Member Posts: 6
edited January 2019 in Radiant Heating
This might seem like a very dumb question, but I'm curious if I need a mixing valve for my planned set up.
I want to run my entire system on 1 pump (grundfos up26-99). I have 2 zones (upstairs and downstairs) with 8 loops per zone (1/2" pex 240-260 ft per loop). 1 zone would be placed about 30' of 1" pex away from the boiler room. I need about .5ish gpm per loop, and I'd like to keep the entire system 1".
I'm using a Navien NCB240, the house is in northern CA so the system is primarily used to maintain temperature, house is 3500 sq ft of 2x6 construction, R23 walls w/ 2" of closed cell and R38 in the rafter. Anyways it seems like I can adjust the temperature and cap the boiler water under 105 degrees or even use their outdoor sensor which has a setting that keeps the boiler water between 80-105 when in use. Or even cap it at 95 degrees in my case.
What I'm seeing is a mixing valve only creates major restrictions to my system. The Taco 5004 I have shows like a 20psi pressure drop at 12-14 gpm... That pretty much renders my oversized pump useless unless I up size the mixing valve to like 1.5" or splurge on a high flow one. Radiant is my only loop in the system, would it be reasonable to just remove the mixing valve and just tee my return to the supply?
  • SuperTech
    SuperTech Member Posts: 2,646
    You should get the Taco I series mixing valve. That will solve all your problems if installed correctly.
  • Rich_49
    Rich_49 Member Posts: 2,785
    732-751-1560
    Rich McGrath 732-581-3833
  • Zman
    Zman Member Posts: 7,611
    You are doing a one temp system with a condensing boiler, correct?
    For this you would not need a mixing valve. Just install the outdoor sensor and do outdoor reset.
    For the pump, I believe boiler has one on board and is designed for primary/secondary.
    For the radiant side, the 26-99 would not be a bad choice on speed one. As long as you don't have much restriction in the manifolds and plumbing, you could probably run a grundfos alpha which is a little less expensive and much more efficient. We would need little more info to help with that one.
    Albert Einstein
    WillTheGreat
  • WillTheGreat
    edited January 2019
    Thanks Zman, that's exactly what I'm doing. One temp with a condensing boiler. I ordered most of the material already, so it's reassuring to know I can save a few bucks and some parts.