Do I need a mixing valve?
WillTheGreat
Member Posts: 6
This might seem like a very dumb question, but I'm curious if I need a mixing valve for my planned set up.
I want to run my entire system on 1 pump (grundfos up26-99). I have 2 zones (upstairs and downstairs) with 8 loops per zone (1/2" pex 240-260 ft per loop). 1 zone would be placed about 30' of 1" pex away from the boiler room. I need about .5ish gpm per loop, and I'd like to keep the entire system 1".
I'm using a Navien NCB240, the house is in northern CA so the system is primarily used to maintain temperature, house is 3500 sq ft of 2x6 construction, R23 walls w/ 2" of closed cell and R38 in the rafter. Anyways it seems like I can adjust the temperature and cap the boiler water under 105 degrees or even use their outdoor sensor which has a setting that keeps the boiler water between 80-105 when in use. Or even cap it at 95 degrees in my case.
What I'm seeing is a mixing valve only creates major restrictions to my system. The Taco 5004 I have shows like a 20psi pressure drop at 12-14 gpm... That pretty much renders my oversized pump useless unless I up size the mixing valve to like 1.5" or splurge on a high flow one. Radiant is my only loop in the system, would it be reasonable to just remove the mixing valve and just tee my return to the supply?
I want to run my entire system on 1 pump (grundfos up26-99). I have 2 zones (upstairs and downstairs) with 8 loops per zone (1/2" pex 240-260 ft per loop). 1 zone would be placed about 30' of 1" pex away from the boiler room. I need about .5ish gpm per loop, and I'd like to keep the entire system 1".
I'm using a Navien NCB240, the house is in northern CA so the system is primarily used to maintain temperature, house is 3500 sq ft of 2x6 construction, R23 walls w/ 2" of closed cell and R38 in the rafter. Anyways it seems like I can adjust the temperature and cap the boiler water under 105 degrees or even use their outdoor sensor which has a setting that keeps the boiler water between 80-105 when in use. Or even cap it at 95 degrees in my case.
What I'm seeing is a mixing valve only creates major restrictions to my system. The Taco 5004 I have shows like a 20psi pressure drop at 12-14 gpm... That pretty much renders my oversized pump useless unless I up size the mixing valve to like 1.5" or splurge on a high flow one. Radiant is my only loop in the system, would it be reasonable to just remove the mixing valve and just tee my return to the supply?
0
Comments
-
You should get the Taco I series mixing valve. That will solve all your problems if installed correctly.0
-
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
You are doing a one temp system with a condensing boiler, correct?
For this you would not need a mixing valve. Just install the outdoor sensor and do outdoor reset.
For the pump, I believe boiler has one on board and is designed for primary/secondary.
For the radiant side, the 26-99 would not be a bad choice on speed one. As long as you don't have much restriction in the manifolds and plumbing, you could probably run a grundfos alpha which is a little less expensive and much more efficient. We would need little more info to help with that one."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Thanks Zman, that's exactly what I'm doing. One temp with a condensing boiler. I ordered most of the material already, so it's reassuring to know I can save a few bucks and some parts.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements