I have 2 1960's vintage thermostats in my house. Are thermostats available that let the room temp dr
MrRogers
Member Posts: 4
Are there modern-day thermostats that allow the room temperature to drop a few degrees before sending the "fire up the boiler" message to the boiler? I would be replacing 1960's era thermostats. Thanks for any helpful info, I appreciate your time!
Look for one that says 'adjustable differential'. That's the difference between the cut-out temperature and the cut-in temperature.
Why do you want to let the temp droop? To keep the sew system operation as close as possible to it's current operation?
And what, besides age, is the matter with the old thermostats?Br. Jamie, osb
Most people consider a differential drop of more than 2deg uncomfortable.
Your old t-stat may have an "anticipator" that you can adjust to a different setting to make your boiler run longer to create longer off periods.
https://inspectapedia.com/heat/Heat_Anticipator_Adustment.php2 -
The anticipator is a hugely un-appreciated piece of mechanical control. It's so much more elegant than a simple dead-band.
Modern dead-band based thermostats will often feel less comfortable than a anticipator based thermostat due to steady state error.
The anticipator essentially actively adjusts the dead-band, so that the longer the heat has been off the tighter the dead-band is, and then same thing when it's on, the longer the heat runs the less overshoot it will allow. A dead-band based thermostat may let the space temp sit 1.5 degrees under the set point for hours making you feel chilly when all you need to feel comfortable is a few minutes worth of heat each hour.
This is all much more noticeable in shoulder seasons where you don't need much heat.3 -
^ Plenty of unused NOS Honeywell T87F Round mercury t-stats available on ebay. Just search for "T87F".0
I just bought two NOS T87F's a couple of days ago off ebay... one for $29 and another for $39. Looking forward to using them with my mod-con.0
My boiler keeps trying to fire back up too soon, then it just turns itself back off. It does that over and over, till it finally actually needs to start up, then it starts and stays running. I'm trying to save the gas valve needless cycling.0
Are you using a programmable thermostat? Do you have it programmed for 1 cycle per hour? They come with a factory default for forced air, which is 5 cycles per hour.MrRogers said:My boiler keeps trying to fire back up too soon, then it just turns itself back off. It does that over and over, till it finally actually needs to start up, then it starts and stays running. I'm trying to save the gas valve needless cycling.
Does the boiler make your hot water as well? Something's not right, but there are a number of other things it could be aside from the stat.
Is this a new thing that started recently?
1960’s thermostat. You guys and your new fangled technology. You need to use a series 10 thermostat from the 20’s with bimetallic strip only.1
- 87.1K THE MAIN WALL
- 58 Biomass
- 117 Chimneys & Flues
- 111 Geothermal
- 163 Indoor-Air Quality
- 72 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 55 Water Quality
