Lochinvar Knight KB106 - zone staying open constant call for heat
gater4456
Member Posts: 4
I would be surprised if it had anything to do with the boiler.
It is more likely a zone control or piping issue.
Can you post more details and pictures?
Albert Einstein0 -
Is it possible that you pinched or damaged a wire for the thermostat creating a short? Possibly in another area of the house0
From your other post, I see you have honeywell valves.
It you slide the lever and encounter no resistance, the valve is open. If there is resistance, the valve is closed. If the valve is pinned in the open position and will not release, you have a bad actuator head.
Those valves have a pretty short life expectancy. They go through motors and end switches far too often. I would suggest buying a few of these and replacing as needed. It is an easy swap and you don't need to drain anything down.
https://www.supplyhouse.com/Honeywell-40003916-026-Replacement-Head-for-V8043E-Zone-Valves-8632000-p"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Zman! Thanks yes you are correct I do have these values and thought they could be the problem. I appreciate the link as well, really helpful!0
How often do they typically go bad?0