Taco ZVC 404 priority stays lit even when not needed.
actonman
actonman Member Posts: 1
The priority zone says it's calling for heat, even though it satisfied. This is preventing my heat zone (1 & 2) from calling for heat. If I turn off the water heater (priority zone) then heat is called for and works. What can make it do this on the priority zone?
  • Do you have zone valves to your heating and DHW zones? It could be a stuck end switch on your DHW zone valve. Happens a lot with Honeywell V8043 zone valves.
  • Ironman
    Ironman Member Posts: 7,829
    edited November 2018
    'Water heater". How about some details and maybe some pics? What type of zone valves?
    Bob Boan
  • SuperTech
    SuperTech Member Posts: 2,633
    Do you actually need DHW priority? My boiler can handle all my DHW usage without using a priority zone, with a single circulator, 41 gallon tank.
  • delta T
    delta T Member Posts: 884
    You can turn priority off using the switch inside the taco zvc404. That will let everything run until you can get it fixed, but I am betting a stuck end switch on your zone valve as @Alan (California Radiant) Forbes said.