Taco ZVC 404 priority stays lit even when not needed.

actonman
Member Posts: 1
The priority zone says it's calling for heat, even though it satisfied. This is preventing my heat zone (1 & 2) from calling for heat. If I turn off the water heater (priority zone) then heat is called for and works. What can make it do this on the priority zone?
0
Comments
-
Do you have zone valves to your heating and DHW zones? It could be a stuck end switch on your DHW zone valve. Happens a lot with Honeywell V8043 zone valves.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
'Water heater". How about some details and maybe some pics? What type of zone valves?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Do you actually need DHW priority? My boiler can handle all my DHW usage without using a priority zone, with a single circulator, 41 gallon tank.0
-
You can turn priority off using the switch inside the taco zvc404. That will let everything run until you can get it fixed, but I am betting a stuck end switch on your zone valve as @Alan (California Radiant) Forbes said.0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 942 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements