Rinnai R85e blew fuses and is now dead
Power surge? If you are really sure you have good incoming voltage and current available, and a good ground, you may be looking at the whole control...Br. Jamie, osb
When i saw the blown fuses a power spike was the first thing that came to mind but nothing else in the house is damaged and no breakers were tripped. I have a second water heater exactly the same as this one. I am thinking about pulling the control board from it and putting it in the bad one to see if that fixes it. I do not want to take the chance of destroying the working one but at the same time I do not just want to start throwing money at it. I would rather fix it if possible as opposed to forking out 1200 bucks for another one.0
I have called several plumbers but none of them in my area seem to be familiar with the internal workings of these water heaters. They just install them.0
call your gas supplier...as far as swapping boards..I'd be nervous doing that...0
Thanks for the replies. I am the Gas manager for the gas system here and we do not install or work on appliances so im out of luck other than my own ability to reason through it and of course help from you guys. I agree with you guys it is to risky so I decided not to swap boards. I do not need 2 of them to work on. I believe i may have found the problem. I found a transformer hidden in the back. It has 120v AC in but nothing coming out. Now i cant find a replacement transformer based on the numbers on the end of it. Anyone have a good place i can cross reference it so I can find a new one? It does not even say what the output is supposed to be so I do not know what I am looking for.0
Can you check the voltage on the other unit?0
Simply swapping boards does not fix the problem. Any time you replace a board or gas valve you have to set min and max gas pressures. Not hard, but do you have a manometer? Your best bet is to call Rinnai 800 621-9419 and have tech serv. get you the part number. Model and Ser # will be req'd.0
Also, with two units it is a good idea to have a cross-over valve/line so you can feed from either one in a pinch.0
Units are on opposite ends of the house so they have separate gas feeds. This one just runs the master bath so luckily the whole house is not down. I do have a manometer so setting gas pressure wont be too hard. I found the exact replacement transformer finally. It breaks 120 VAC down to 100 VAC. Right now the bad one has 120 VAC in and 0 VAC out. The working unit has 120 VAC in and 99 VAC out. Rinnai does not want to talk to me because I m the homeowner so I will have to get a plumber to call them for me. That is probably the best course of action. Thanks for all your input on my problem guys. Will let you know how it comes out.0
If the fuses blew it could be the transformer shorted out and then the thermal fuse inside the transformer opened up at about the same time the fuses popped. With the fuses opened up measure the resistance of the transformer primary on both units, then measure the resistance of each secondary.
3PSI gauge0 -
The transformer is definitely dead so I am going to start there and hopefully that will get it back online.0
Not to be a buzzkill, but I'd be concerned as to why that transformer is dead, seems kind of odd that it would die and take out the fuses with it. I'd expect it to just open.
Did you ohm the transformer out? Did you ohm out what the transformer drives?
I just don't want to see you put a new transformer in and see it go up in smoke if you can avoid it.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
manuals
https://rinnai.us/customer-care/manuals-literature
not a lot on wiring or troubleshooting, geez
I believe a power surge got it. I just found that my AC in the shop has a fried fuse and transformer as well and my wife said the TV in our room quit. There was a pretty bad lightning storm here last weekend. And im with you on the manual. There is not much help in it for the trouble shooting on the wiring. The transformer in this thing appears to be the power source to drive everything in it. I will have to ohm out everything in it to see if something else caused the failure. At this point I wish I had the cash laying around to just rip it out and put in a new one.1
I live high on a hill in Ct, lightning all around, I have two whole house surge suppressors, after a storm years ago took out a tv, toaster, computer and printer.
I rec'd them highly especially since electricity isn't a very good product anyway, everything lasts longer, especially light bulbs.
http://www.thisoldhouse.com/toh/article/0,,387874,00.html
They are very easy to install or have an electrician do it if you are not comfortable around the main box, safety #1.0 -
A couple of years ago I installed a whole house surge protector, it feeds off a 50A breaker. They are useless against a direct strike but they will swallow a lot more than the puny MOV's that you usually see in equipment. They really aren't that expensive so it might be worth looking into.
3PSI gauge0 -
Send me a pm with your email address.0
I will definitely look into purchasing a surge protector. This is a major pain trying to fix this water heater. Rinnai will not talk to me as the homeowner or as the gas technician. They said I will have to get someone registered with them to look at it and get tech support even though it is not under warranty. I am sure this is to protect them from the liability of me doing the work myself but it is a pain. I put a new transformer in it and when i turned the power on it blew the fuses again. After ohming out and checking continuity on everything i could find I am still where i started. If i hire someone to work on it and after buying parts I will have as much in this one as a new one so I am going to order a new one and scrap this one out. I appreciate the input everyone.0
Name one company that will.Hatterasguy said:Lesson learned:
Don't buy Rinnai.
Any company that will not assist in troubleshooting their product with a competent individual should not get your business.
They have made the conclusion that NOBODY is competent other than their own chosen installers. So be it.
Tell 'em to pound sand. There are plenty of other units that are suitable.
Just one.
HTP....AO Smith.....Dunkirk.......Sanyo/Panasonic....Fujitsu and more.
I am not a "licensed dealer" for any of the above; tech support must have deemed me competent over the phone with our conversation.
Slow typer.....had to check spelling on Fujetsou.0 -
I see.
HG, Rinnai will talk with anyone who is licensed to perform the work. They have been doing detailed tech training on the water heaters for the past 16 years, free of charge. How does a guy on the tech line know that the guy is capable? It is a sophisticated GAS appliance after all.0
Easy.Jack said:HG, Rinnai will talk with anyone who is licensed to perform the work. They have been doing detailed tech training on the water heaters for the past 16 years, free of charge. How does a guy on the tech line know that the guy is capable? It is a sophisticated GAS appliance after all.
When you ask him to grab a manometer and he says "a what?" you know he's not capable.
We've talked people through troubleshooting antique refrigerators with damaged float valves via nothing more than text. It's fairly easy to tell when someone isn't capable of something.
Anyone know anything about EcoTemp? One of my suppliers carries them and tells me they are a good product but if anyone knows anything about them I would like to hear it.0
I could understand Rinnai not wanting to deal with me if it was warranty work but the fact that it is out of warranty and i shelled out a lot of money on their products I would think a little help would be in order. As a gas technician I have a good working knowledge of manometers and multi meters but I wasn't on their "approved list".0
You not being able to work on it means you'd either need to buy a new one, or hire someone to fix it. Being hiring someone to fix it is highly unlikely, you'll just go buy a new one and they like that.StevenS said:I could understand Rinnai not wanting to deal with me if it was warranty work but the fact that it is out of warranty and i shelled out a lot of money on their products I would think a little help would be in order. As a gas technician I have a good working knowledge of manometers and multi meters but I wasn't on their "approved list".
That's my opinion on it anyway.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
I am a plumbing /heating contractor myself and we have a lot of Rinnai heaters and water heaters around here, and I have to say, whenever I have needed tech support, which hasn't been often, they have been excellent. They answer the phone right away and will stay on until the problem is resolved. Not sure why the op couldn't get any help from them, but I will definitely keep buying them because I know they will be there for me and the products are great.
Also, I had to go do a warranty call on one a few years ago and they paid my bill for labor, which totally shocked me because nobody pays labor. Top notch company in my opinion.
So, that is my plug for Rinnai.
Rick1 -
I have no doubt that tech support from Rinnai is good if you are an approved technician. It has lasted 8 years trouble free so I am not badmouthing their products or tech support either for that matter. It is just a matter of them not giving ME tech support. All of the reputable plumbers around here charge an average of $125 an hour with a 2 hour minimum, which I have no problem with when I need a plumber. Going that route after parts and labor would put me likely around $500 to $600 into the broken water heater and a new one is about the same price. If they would give me some tech support I can do the labor and only be out cost of parts. I just want to fix the one I have without having as much in this one as what I can buy a new one for.0
Hello: Their system seems flawed, clearly! How about a work-around? Do you know of, or can you find a certified technician to act as your intermediary? Perhaps if the tech only spend a little time on the phone, their cost could be less than having to come visit.
Yours, Larry0 -
I am in negotiations with a plumber I have used before to do that for me. Will let you know how that works out. Thanks for the input.0
Yes. He is a plumber i have used on jobs at work and he said he is on their list and has been through Rinnai training so they should talk to him. Only issue is he said when on the phone with tech support they require him to be in front of the unit. So we are negotiating his rate now. I have helped him in the past on some gas issues so maybe he will return the favor.0
It has been narrowed down to the circuit board. I will order a new one Monday. Thanks for all your help guys.0
Hi StevenS, I hope you're still around two years later to see this.StevenS said:It has been narrowed down to the circuit board. I will order a new one Monday. Thanks for all your help guys.
I also have an R85 with a bad transformer, which also blew both fuses. The secondary winding is open (infinite resistance). I'm searching for a replacement transformer now. In case my issue turns out the be the same as yours, can you tell me where you found a replacement control board for order?0 -
I don't know anything about Rinnai but I would question why the secondary is open. Did something cause that? It's rare for a winding to just open on its own.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Thanks for the reply. Unknown what could have caused it. The service manual doesn't list any diagnostic tests for such a condition. I could check impedance on the circuit(s) the transformer feeds to see if something is shorted there.ChrisJ said:
The Rinnai diagnostic manual says to replace the transformer if it's found to be faulty. So that will be step #1
In the time since my initial post, I found a source for a replacement control board. If it turns out the new transformer doesn't solve the issue, I'll give that a try.
Update: My bad. It's the primary winding that's open, not the secondary. I checked impedance where the secondary feeds to control board anyway. It started ~14Mohm and steadily dropped (I assume from a cap charging). So I think that's okay. Or at least not the cause of the bad transformer.
Maybe 60hz vibration eventually caused a winding to rub through the shellac coating causing a short, which in turn blew an internal protection mechanism inside the transformer?
Installed a new transformer. The 3 amp fuses blow immediately. The solenoids and igniter pass impedance tests. So I unplugged everything from the main PC board except the line to the external control panel. It still blows the fuses immediately. I can't check the individual components on the main board because it's potted. So I've ordered a replacement board.0
Sounds like you did what you could.
Potted boards suck for that reason.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Can you tell me where you ordered the transformer and board? Similar problem. Dead at the control terminals. From this thread I see that voltage should be 100vac on the secondary.0
