Weil-McLain EG-50 (repipe job)
Dave0176
Member Posts: 1,178
With this job the boiler is waaay oversized, don’t understand the reasoning behind installing such a large boiler, however the current HO inherited it when he purchased the home two years ago. He said the heat was terrible, very uneven, very noisy, boiler was very dirty. He hired a plumber who came in for a cleaning, he claimed he skimmed and added squick flushed it a few times and left.
HO called me, I did an EDR first and came up with 280 EDR load against the boilers output of 454 EDR, so I recommend a two stage gas valve and a repipe because the piping wasn’t great. We did it in stages with the gas valve last winter and now the repiping. Boiler manual calls for 1) 2-1/2 riser into a 2-1/2 header, however this as far as I’m concerned is waaay too small so in goes 2) 3” risers about 40” above the water line into a 3” header with a 2” equalizer.
Also during a recent kitchen renovation someone installed a radiator or should I say repiped and moved a radiator, anyway they pitched the pipe towards the radiator so you know how well it drains condensate. I’m going pull the pipe down which will put the pipe below the main, so to remedy this it will be dripped into its own return.
To get the old plug out of the boiler I cut it in half with a sawzall then made two vertical cuts, then a chisel and hammer and caped it right out easily.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
1
I prefabbed the header in my garage, takes the bulk of the work away on the job.
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
All finished and working beautifully.....
Is this a two-pipe system? If so, where did you vent the condensate return side to atmosphere?0
Single pipe steam Zack.zackwatt said:Is this a two-pipe system? If so, where did you vent the condensate return side to atmosphere?
- 109 Chimneys & Flues
- 5.6K Gas Heating
- 970 Plumbing
- 385 Solar
