To Be Or Not To Be
An appropriate title I should think for an old theatre. The steam and it's boiler have been long gone. The seating area was converted to hot water. But the stage and the dressing rooms beneath the stage were not, and have no heat at all.
Complicating matters is that the boiler room is in the front of the theatre, and of course the stage and dressing rooms are at the back. Not a whole lot of EDR for the stage and dressing rooms by themselves, but twice as much to get the steam there from the front 2 * (4" pipe * 150').
So the question is: Is there to be steam heat once again? Or is steam heat not to be?
Stay tuned...
New England SteamWorks
newenglandsteamworks.com
    Steamhead Member Posts: 18,184
    Hoffman Vapor. That should be a no-brainer- fix the steam.
    Consulting
    delta T
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,682
    A cakewalk for you.
    Retired and loving it.
    Jim_R
  • Fred
    Fred Member Posts: 8,542
    Easy answer: "tis nobler in the mind to suffer
    The slings and arrows of outrageous fortune,
    Or to take arms against a sea of troubles,
    And by opposing, end them" Let there be Steam!
    Erin Holohan Haskelldelta TNew England SteamWorks
    Jamie Hall Member Posts: 26,783
    Agreed. And since you are known to know what you are doing, it shouldn't be that hard! The only comment I would make is... insulate the dickens out of the supply mains. Also... does it still have the crossover traps? And if not, can they be replaced and all other vents closed except the main vents on the return? If so, I would very seriously consider -- despite the expense -- using Hoffman 76s. Granted that they are slower than say a Gorton would be, never mind a BigMouth, and they certainly aren't cheap -- but they will allow the system (if you get rid of leaks!) to pull a substantial vacuum between boiler runs, which may help in getting steam to the backstage area more evenly.
  • gerry gill
    gerry gill Member Posts: 3,083
    Restore!!!!!!!!!!!!! and take pride in getting paid to have FUN!
    gwgillplumbingandheating.com
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,362
    Wow! How old is the building? Such history there. Looking forward to seeing the "after" photos too.
    President
    HeatingHelp.com
    With that version of the Differential Loop, and that main vent, I'd say mid to late 1920s............................
    Consulting
    Thanks, @Steamhead.
    President
    HeatingHelp.com
  • brandonf
    brandonf Member Posts: 224
    Which theater is it? I'm from Providence. 😎
    Homeowner, Entrepreneur, Mechanic, Electrician,
    "The toes you step on today are connected to the butt you'll have to kiss tomorrow". ---Vincent "Buddy" Cianci