To Be Or Not To Be

Options
An appropriate title I should think for an old theatre. The steam and it's boiler have been long gone. The seating area was converted to hot water. But the stage and the dressing rooms beneath the stage were not, and have no heat at all.

Complicating matters is that the boiler room is in the front of the theatre, and of course the stage and dressing rooms are at the back. Not a whole lot of EDR for the stage and dressing rooms by themselves, but twice as much to get the steam there from the front 2 * (4" pipe * 150').

So the question is: Is there to be steam heat once again? Or is steam heat not to be?














Stay tuned...
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com

Comments

  • Steamhead
    Steamhead Member Posts: 16,843
    Options
    Hoffman Vapor. That should be a no-brainer- fix the steam.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    delta T
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,528
    Options
    A cakewalk for you.
    Retired and loving it.
    Jim_R
  • Fred
    Fred Member Posts: 8,542
    Options
    Easy answer: "tis nobler in the mind to suffer
    The slings and arrows of outrageous fortune,
    Or to take arms against a sea of troubles,
    And by opposing, end them" Let there be Steam!
    Erin Holohan Haskelldelta TNew England SteamWorks
  • Jamie Hall
    Jamie Hall Member Posts: 23,324
    Options
    Agreed. And since you are known to know what you are doing, it shouldn't be that hard! The only comment I would make is... insulate the dickens out of the supply mains. Also... does it still have the crossover traps? And if not, can they be replaced and all other vents closed except the main vents on the return? If so, I would very seriously consider -- despite the expense -- using Hoffman 76s. Granted that they are slower than say a Gorton would be, never mind a BigMouth, and they certainly aren't cheap -- but they will allow the system (if you get rid of leaks!) to pull a substantial vacuum between boiler runs, which may help in getting steam to the backstage area more evenly.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    New England SteamWorks
  • gerry gill
    gerry gill Member Posts: 3,078
    Options
    Restore!!!!!!!!!!!!! and take pride in getting paid to have FUN!
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,293
    Options
    Wow! How old is the building? Such history there. Looking forward to seeing the "after" photos too.
    President
    HeatingHelp.com
  • Steamhead
    Steamhead Member Posts: 16,843
    Options

    Wow! How old is the building? Such history there. Looking forward to seeing the "after" photos too.

    With that version of the Differential Loop, and that main vent, I'd say mid to late 1920s............................
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Erin Holohan Haskell
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,293
    Options
    Thanks, @Steamhead.
    President
    HeatingHelp.com
  • brandonf
    brandonf Member Posts: 205
    Options
    Which theater is it? I'm from Providence. 😎
    Homeowner, Entrepreneur, Mechanic, Electrician,

    "The toes you step on today are connected to the butt you'll have to kiss tomorrow". ---Vincent "Buddy" Cianci