Proper nozzle?
georgede54
Member Posts: 55
I have a Burnham boiler Model # PV8 5 ST HBUR.
Does anyone out there know what is the proper nozzle for use with that model?
Thanks.
George
Thanks.
George
What burner is on it?All Steamed Up, Inc.
Consulting1 -
Thank you for getting back to me.
Other than by giving you the model number, I'm not sure how to tell what burner it is on.
How would I find out?
Thanks,
George0 -
Post a picture of the burner.
As @GBart alluded, there's a lot more to safely running your burner than just changing the nozzle. The first one being that you also need to know the fuel pump pressure.There was an error rendering this rich post.
And, after doing any work on a burner it must be tested with a digital combustion analyzer. This is a safety issue.
If your present service company is not testing the burner, they do not deserve your business.All Steamed Up, Inc.
Consulting4 -
Thanks one and all. I was never considering replacing it myself. But I think it's all been straightened out.0