piping 2 water heaters in series

mikedo
mikedo Member Posts: 174
is their any drawbacks to piping 2 fifty gallon water heaters in series. i have limited height and 1" feed for cold water

Comments

  • DZoro
    DZoro Member Posts: 1,048
    nothing wrong with it, if you have the need for 100 gallons of hot water on a constant basis. May want to consider a on demand system.
  • hot_rod
    hot_rod Member Posts: 22,022
    No problem with series. We commonly did that with vacation homes, turn the 1'st one to vacation setting until the home is at full occupancy.

    The first tank will see most of the mineral and sediment build up.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Ironman
    Ironman Member Posts: 7,367
    Are we talking gas or electric?

    If it’s gas, the second one will see a decrease in efficiency because of the hotter water temp entering it.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • JohnNY
    JohnNY Member Posts: 3,226
    I've never been a fan. Pipe them in parallel and they'll wear evenly and at half the demand put on the first tank in the series piping configuration.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Canucker
  • hot_rod
    hot_rod Member Posts: 22,022
    If you do want to pipe parallel 3 piping choices are, reverse return, "moose antler, or add a balance valve on both tanks to balance draw evenly. The balance valve option may help with your piping limitation issue.

    This drawing happens to be indirect with balance on the coil and potable water side.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,273
    Hello, My experience with parallel piping is often they get thrown out of balance just by corrosion or rust happening where nipples are screwed into the tanks or from dielectrics. If you can temperature balance the system periodically, parallel is fine. Otherwise, (as long as flow remains OK) series with bypass valves on each tank is my preferred way. ;)

    Yours, Larry

    ps, Water in my area can get pretty bad and that has everything to do with the sort of problems I see. If you have good, not very conductive water, there may be no problem down the road, going parallel.
  • hot_rod
    hot_rod Member Posts: 22,022

    Hello, My experience with parallel piping is often they get thrown out of balance just by corrosion or rust happening where nipples are screwed into the tanks or from dielectrics. If you can temperature balance the system periodically, parallel is fine. Otherwise, (as long as flow remains OK) series with bypass valves on each tank is my preferred way. ;)

    Yours, Larry

    ps, Water in my area can get pretty bad and that has everything to do with the sort of problems I see. If you have good, not very conductive water, there may be no problem down the road, going parallel.

    Good point Larry, dielectric unions are notorious for corroding closed. With a 132 Quicksetter you could observe and re-balance from time to time :)
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mike
  • mikedo
    mikedo Member Posts: 174
    thanks I'm just going to pipe them in series
  • JohnNY
    JohnNY Member Posts: 3,226
    hot rod said:

    With a 132 Quicksetter you could observe and re-balance from time to time :)

    Or you can pipe them in parallel and never think about it again.

    @mikedo You're doing yourself a disservice by going with series piping. But whatever.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    GBart
  • GBart
    GBart Member Posts: 746
    edited July 2018
    I was taught that parallel was the only way, there is reference material to back this up. In parallel the supply and outlet piping to each unit must be exactly the same and they must be equal units. In series the first unit typically does all the work, this can work if you are doing solar-another water heater, gas fired feeding electric, etc or if you have non matching size tanks. Piping in series usually causes the first tank to fail way before the other.

    Another option for series is a water heater piped to a aqua-booster to increase storage using the first heater to supply the aqua-booster.

    http://www.texasinspector.com/files/Water-Heater-Plumbing.pdf



  • hot_rod
    hot_rod Member Posts: 22,022
    GBart said:

    I was taught that parallel was the only way, there is reference material to back this up. In parallel the supply and outlet piping to each unit must be exactly the same and they must be equal units. In series the first unit typically does all the work, this can work if you are doing solar-another water heater, gas fired feeding electric, etc or if you have non matching size tanks. Piping in series usually causes the first tank to fail way before the other.

    Another option for series is a water heater piped to a aqua-booster to increase storage using the first heater to supply the aqua-booster.

    http://www.texasinspector.com/files/Water-Heater-Plumbing.pdf



    If the first tanks fails earlier, seems the second tank lasts much longer, isn't it sixes at that point :) ?

    Any data to support the first tank failing way before the second?

    In our rental/resort applications series made more sense and I don't recall the failure rate you suggest?

    I'd highly encourage HW users to run tanks at 140 for bacteria reasons, so I doubt efficiency would be much different between first and second tank, we are talking 70% efficient appliances typically with standard tank heaters.

    I hate seeing bullhead tees, even on domestic water piping, as the parallel drawing shows. It doesn't take much flow resistance, as Larry mentioned to put them out of "balance"

    Series is nicer for recirc as you just circulate thru one tank.

    Seems like Rheem is fine with either piping method.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • GBart
    GBart Member Posts: 746
    The first one does all the work, ergo it has more run time ergo it fails first, it's in several documents on line
  • jumper
    jumper Member Posts: 2,228
    GBart said:

    The first one does all the work, ergo it has more run time ergo it fails first, it's in several documents on line

    all depends. First one runs cooler? Series is often said to be no no but I don't see why.
  • hot_rod
    hot_rod Member Posts: 22,022
    GBart mentioned parallel piping is the only way and you have reference material to back it up?

    The Rheem doc you attached seems to show series as an option? Although it shows a gas and electric In series, much different recovery rate tanks.

    Generally two tanks are used to cover large dump loads like filling a 100 gallon soaking tub for example, or multiple showers running at the same time, as in ski resort rental properties.

    So both tanks get pulled down to 100 f or lower. Under that type of use pattern I don’t see a much shorter life expectancy in the first tank. Consider tanks are engineered to a 6-7 year warranty these days.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • JohnNY
    JohnNY Member Posts: 3,226
    Why is there even a discussion on this? When you install multiple tanks/boilers/etc in parallel and fire them up from a cold start, you can watch and hear them fire up and shut down within seconds of each other. Forget about balancing valves. They're not needed. Isolation valves will do, and only if you want to include them. Setting the tanks at different temperatures is a guess at what's going to work best.
    Install them in parallel, same temperature, full flow (ie. half to each, naturally occurring), and you're done.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.