Backflow Preventer for Condensing Model install with PVC?
I am installing eight new Takagi tankless water heaters--the condensing models that require 3" PVC. I am installing 8 of them as a gang, with gang ventilation, per the manual. My installer insists that each unit must have a back flow preventer installed on the exhaust. I argue that back flow preventers are for the non-condensing models with the expensive stainless vent pipe. IN fact, I don't see any back flow that is not stainless, so it would be wrong for PVC.
Who is correct?
The whole reason I spent more on condensing models is the cheaper easier PVC exhaust issue. I wanted them installed per the manual, eight max, into the same main exhaust pipe. Nothing he says makes sense to me.
I need this answered urgently, because if I'm right, I need to know if I should lose faith in this guy. I'm not sure he knows what he's talking about, but I need to know the answer to this issue ASAP. I'd appreciate any help I can get. He tried to talk me into Navien brand, which raised my suspicion in the first place. He is my primary contractor's plumber, so I am stuck with him for now.
  • lchmb
    lchmb Member Posts: 2,997
    http://www.takagi.com/media/62108/2000536265.pdf page 26 shows a non return valve and gives the part number.. this is on the condensing unit..not sure if it's what you have
    delta T
  • Ironman
    Ironman Member Posts: 7,844
    The proper term is "back draft", not backflow. A back flow preventer goes on the potable water line feeding a boiler. I'm not trying to be critical - just to avoid confusion.
    Regardless, every common vent condensing boiler that I'm familiar with requires some form of back draft protection.
    Bob Boan
    delta TRobinInCali
  • Zman
    Zman Member Posts: 7,611
    The instructions on page 26 shows the venting diagram, which must be followed for a safe warrant-able installation. The "non return" valve is shown on page 10. It is made of PVC so is certainly intended for a condensing application.
    Albert Einstein
  • RobinInCali
    RobinInCali Member Posts: 54
    Thank you all for this. I see that my plumber had the wrong term. The only negative about this thing is that we have 8 tankless units, so we need 8 non-return valves. That's about $3,000 I didn't know I had to spend. Insert Sad Face Here.