Backflow Preventer for Condensing Model install with PVC?
RobinInCali
Member Posts: 54
I am installing eight new Takagi tankless water heaters--the condensing models that require 3" PVC. I am installing 8 of them as a gang, with gang ventilation, per the manual. My installer insists that each unit must have a back flow preventer installed on the exhaust. I argue that back flow preventers are for the non-condensing models with the expensive stainless vent pipe. IN fact, I don't see any back flow that is not stainless, so it would be wrong for PVC.
Who is correct?
The whole reason I spent more on condensing models is the cheaper easier PVC exhaust issue. I wanted them installed per the manual, eight max, into the same main exhaust pipe. Nothing he says makes sense to me.
I need this answered urgently, because if I'm right, I need to know if I should lose faith in this guy. I'm not sure he knows what he's talking about, but I need to know the answer to this issue ASAP. I'd appreciate any help I can get. He tried to talk me into Navien brand, which raised my suspicion in the first place. He is my primary contractor's plumber, so I am stuck with him for now.
Who is correct?
http://www.takagi.com/media/62108/2000536265.pdf page 26 shows a non return valve and gives the part number.. this is on the condensing unit..not sure if it's what you have1
The proper term is "back draft", not backflow. A back flow preventer goes on the potable water line feeding a boiler. I'm not trying to be critical - just to avoid confusion.
Regardless, every common vent condensing boiler that I'm familiar with requires some form of back draft protection.Bob Boan
The instructions on page 26 shows the venting diagram, which must be followed for a safe warrant-able installation. The "non return" valve is shown on page 10. It is made of PVC so is certainly intended for a condensing application.lchmb said:http://www.takagi.com/media/62108/2000536265.pdf page 26 shows a non return valve and gives the part number.. this is on the condensing unit..not sure if it's what you have
Albert Einstein0 -
Thank you all for this. I see that my plumber had the wrong term. The only negative about this thing is that we have 8 tankless units, so we need 8 non-return valves. That's about $3,000 I didn't know I had to spend. Insert Sad Face Here.0
- 116 Geothermal