HEADER AND EQUALIZER ARE THE SAME SIZE
PhilDavid
PhilDavid Member Posts: 68
Just replaced a faulty gas valve on a Burnham IN7S that was installed by another company and noticed the equalizer was the same size of the header...2”. I know that’s not in line with the manufacturers specs, but will that make a difference?
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    I would download the installation manual, and show the owner what size pipes should have been used, in order for correct operation, and warranty coverage.
    Such a small riser will surely raise the velocity of the exiting steam, and blow a lot of water up into the mains, reducing efficiency.—NBC
  • Dave0176
    Dave0176 Member Posts: 1,177
    No that boiler would require two 2” riser and a 3” header minimum. But hey at least the equalizer is big enough to route all the water back to the boiler. Lol
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • PhilDavid
    The header should have been 3” then reduced to 1-1/2” on the drop for the equalizer... I know... this isn’t piped right to begin with. But is piping the equalizer the same size as the header detrimental in the long run? Boiler works fine, no issues
    Just too curious I guess
  • Dave0176
    No not at all, in fact regardless of what the manufacturer says most of us guys here run a 2” equalizer minimum.
    EBEBRATT-Ed Member Posts: 15,573
    Risers, equalizers and headers can always be larger than specified in the install manual. The install manual sizes are minimum. In this case the oversized equalizer could be helping the cause
  • PhilDavid
    Good to know. Thanks!