Boiler Feeder Check Valves?
Major7
Member Posts: 44
Greetings:
I'm about ready to repipe my boiler feeder, since the dielectric unions were not installed in the right place by the contractor (before I purchased the house). My question is simply this, is a check valve required, and if so, what if any type venting mechanism is required? My home is in the US.
Yes an back flow preventer is required. on any boiler feeder connected to the water supply ...
thanks for the feedback. Is a check valve a suitable backflow preventer?0
Check your local code. Here in Omaha, we would need a testable backflow, even though I have a spring loaded valve on the feed. The backflow must also be checked for operation yearly, but your requirements may vary in your location.—NBC0
Nicholas, is that a city of Omaha or state of NE requirement.
Is annual testing/certifying required?
Our small local water dept says boilers must have a testable BFP.
Most of the pictures we see (other states) here have only the double check air gap BFP installed.0 -
Generally speaking, a check valve is not acceptable as a backflow preventer -- and honestly even if it were I wouldn't accept it on my own plumbing, nor ever install one on someoneelse's.Br. Jamie, osb
But is it testable?.....I think not.
Is it adequate protection......I think so.0 -
Do you need the 1156f if its a steam boiler.... the 9d should suffice.0
9D is fine in MAss unless you have glycol or chemicals in the boiler. I'm not a plumber but that's what plumbers in our shop told me0