Not enough hot water--need help!

Options
124»

Comments

  • HomerJSmith
    HomerJSmith Posts: 2,834
    edited February 2018
    Kunisk, how about some accurate temperature measurements on the boiler input and output of the tank. Take a measurement when you start to draw hot water and the boiler commences to fire. Take another reading when the tank begins to run out of hot water.
    Mark Eatherton
  • HomerJSmith
    HomerJSmith Posts: 2,834
    Here's a thought, maybe there's a manufacturing defect in the tank and there isn't a dip tube in it and it isn't stratified.
  • @HomerJSmith



    Well done.
  • Grallert
    Grallert Posts: 1,217
    Assuming that 6:00 on Homers diagram is the front of the tank It looks like OP's tank is piped wrong. But then it wouldn't work at all would it?

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver