Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Not enough hot water--need help!

Options
124»

Comments

  • HomerJSmith
    HomerJSmith Member Posts: 2,441
    edited February 2018
    Options
    Kunisk, how about some accurate temperature measurements on the boiler input and output of the tank. Take a measurement when you start to draw hot water and the boiler commences to fire. Take another reading when the tank begins to run out of hot water.
    Mark Eatherton
  • HomerJSmith
    HomerJSmith Member Posts: 2,441
    Options
    Here's a thought, maybe there's a manufacturing defect in the tank and there isn't a dip tube in it and it isn't stratified.
  • SeymourCates
    SeymourCates Member Posts: 162
    Options
    @HomerJSmith



    Well done.
  • Grallert
    Grallert Member Posts: 644
    Options
    Assuming that 6:00 on Homers diagram is the front of the tank It looks like OP's tank is piped wrong. But then it wouldn't work at all would it?
    Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker