Lochinvar Induction Fan Puzzle
ced48
Member Posts: 469
I have a 5 year old Lochinvar WH55 that has developed an interesting habit. When the outlet temperature reaches 150 degrees on a DHW call, or running in service mode, and hitting that temperature, the induction fan begins to do a little whistling, and slight air rushing sound-Increasing the pump speed, thus lowering delta-t, stops it, as does covering the side air intake. Any ideas on this one?
What do you have for gas piping? Is your domestic water outlet set for 150*?0
Sorry my bad, what is your max temp for the boiler set at?0
How long since cleaning and maintenance was done?Bob Boan
I just cleaned the heat exchanger, burner, and checked combustion levels. I also replaced the fan gaskets. The boiler was more or less clean, little bit of debris.
Max boiler 180-0 -
Was it doing it before you did the maintenance? Double check all the bolts make sure everything is tight.0
Yes, that why I did the maintenance-0
is this a new problem, or has it been doing for a long time? Seems to me you need a combustion analyzer to tune the combustion a bit. After 5 years, even if it was set up perfectly on install, it most likely needs a little tweek on the combustion settings. Do you have steel pipe for the gas supply all the way to the unit, or is it connected with a short flexible gas supply?0
Newish problem, it's minor-I have an analyzer. Propane- Co2 10.6 Co 75 high fire. Low fire Co2 10.6 Co 22-Steel pipe, no flexible connector-0
Did you clean the water side? If not, I'd get some Fernox boiler cleaner and run it through and flush the system.Bob Boan
No, only the fireside-Is this difficult to do?0
No, just follow the pictorial instructions on the can. Obviously, you have to put it in the system with no pressure on it.Bob Boan
Bob-I just got the water some quality numbers from our town water department. To me, they look real good. Chloride 23ppm, pH 8, Chlorine .68 ppm, TDS 56-74 , and hardness 35.7ppm
Is not the Co2 of 10.6 pushing it for propane? Seems high0
10 .0 to 11.0-0
BTW you need 140F in your tank to prevent legionella!0