central home oil heater exhaust and damper adjustment
The Dwyer mark II is the cheapest manometer that i can find resolution down to 0.01 and it has great user ratings. Comments?
bryant install paperwork gives no info on exhaust. beckett paper work says 1/4" rise for every 12", might need an exhaust fan to pull the exhaust out, if exhausting to out side of building, it's better to have the combustion air intake going thru the same wall to balance the unit. I dont understand that and it has worked fine all these years with intake in garage, exhaust outside roof.
comments?
pics https://imgur.com/a/6pxXn
tks,
pa
You're using the wrong pipe for the flue, and you can't use that amount of length to get thru the roof. By code it's all wrong. Once you get thru the roof you'll need to be 2.5' higher than anything within 10 ft.
This isn't a DIY project. You need someone who will do it correctly.There was an error rendering this rich post.
why are u moving your flue?"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
installation 12 years ago was by licensed contractor and it passed city inspection.
because I want if off the roof. reason is not relevant.0 -
No problem with the reason; that's your choice. However... you are going to have to do the new venting correctly according to code, the boiler manual, and you local authority having jurisdiction. I have serious doubts that the smaller longer exhaust vent which you are proposing will meet any of those three. If the boiler is not intended to be used with an induced draught fan, it can't be, and that's that -- and no clever magic with dampers will change either one.Br. Jamie, osb
bryant install paperwork gives no info on exhaust. beckett paper work says 1/4" rise for every 12", might need an exhaust fan to pull the exhaust out0
It probably tells you to install & vent it according to NFPA 31 & NFPA 211paulmars said:bryant install paperwork gives no info on exhaust..., might need an exhaust fan to pull the exhaust out
Keep hacking away...
The folks here on this site are for the most part professionals and very safety conscious. We all see an unsafe situation judging by your picture. Most here are willing to offer a work around as long as the solution is safe. It really is all about doing a job correctly and with the home owners well being paramount.
2 -
I haven't gotten any yet.Grallert said:The folks here on this site are for the most part professionals and very safety conscious. We all see an unsafe situation judging by your picture. Most here are willing to offer a work around as long as the solution is safe. It really is all about doing a job correctly and with the home owners well being paramount.
No? Well, you have, but perhaps you didn't care for what was said. We can't help that. Good luck.paulmars said:Br. Jamie, osb
You just want to do it no matter if it's wrong and against code?
Then just do it. If your house burns down or someone dies from CO poisoning, you're on the hook for doing it wrong. Pleading ignorance doesn't relieve you from liability.
2 -
Ive read NFPA 31 and 211 and my city code requirements. I dont see violations with my current system and it looks like my modification is acceptable.0
At least he is still alive...
And you read it wrong...There was an error rendering this rich post.
- 87K THE MAIN WALL
- 58 Biomass
- 113 Chimneys & Flues
- 109 Geothermal
- 161 Indoor-Air Quality
- 994 Plumbing
- 389 Solar
