Fin tube ratings
Dave0176
Dave0176 Member Posts: 1,178
edited January 2018 in Strictly Steam
Hi all, I unfortunately ran into a one pipe boiler replacement where the HO removed most of the CI radiators and replaced it with slant fin steel 1-1/4 baseboard in the standard type baseboard enclosure. He said they had this done in 1968 so they been there a while. The longest run is the dinning room at 10 ft. I need the steam output ratings for these.
I asked if they hammer and he said the dinning room one does sometimes. Anyway I got make sure steam velocity is kept super low keep these as quite as possible. Their both 80 yo so the baseboard will be staying.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
    Jamie Hall Member Posts: 26,830
    You can get pretty darn close with arithmetic -- find the area of a fin (count both sides! -- subtracting for the pipe) and then count the number of fins per foot and multiply -- and that will be pretty close to the EDR per foot (do all this in feet and square feet, of course).
  • JohnNY
    JohnNY Member Posts: 3,339
    edited January 2018
    Hi Dave,
    I'd do this: BTU/ft ÷ 240 = sq. ft. EDR
    Best,
    John
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Dave0176
  • Dave0176
    Thanks guys appreciate it. I figured what they have, it’s the multi pack 80 style with steel fins so according to slant fin 990 btu, regardless, the boiler size I chose is the right size.
    EBEBRATT-Ed Member Posts: 19,551
    I was going to suggest just looking up some baseboard. For a given pipe size and fin area that would be close enough. What @JohnNY & @Jamie Hall suggested is fine although the "bare ratings" @JohnNY gave you will be reduced by the baseboard enclosure.
    If the long one bangs you could make it two pipe if you can drip it to a wet return or drop a loop to the floor and come back up in the bottom of the steam main..........but you already know that
  • Dave0176
    Ed I appreciate the thoughts and yes I am familiar with running baseboard on one pipe steam, that being said the HOs are in their 80s the baseboard has been there 50 years they just want me to replace the 70 year old boiler.
  • JohnNY
    I'm not so sure that's right. Often, the enclosures influence convection and therefore heat output. I don't know how the manufacturer determined these ratings but for a quick EDR calculation, I'd think you could do a lot worse than using the (given) BTU-to-EDR multiplier.
    Classes
    @JohnNY you are correct.
    I was thinking wrong on that one. The baseboard enclosure gives it the chimney effect. Bare element gives off less heat.
    I knew it influenced the rating but I was wrong about which way. Sorry :):)
  • Dave0176
    Yep Slant Fins info gives both the bare element and the enclosure outputs. Once again guys thanks a bunch.