can anyone identify this main steam vent valve?
rhodebump
Member Posts: 155
It's a 3/8 inch size. I plugged the vent for now, but I would like to order a replacement.
Here is a picture:
Would any 3/8 steam vent work such as:
https://www.supplyhouse.com/Gorton-G18-Gorton-No-1-3-8-Air-Eliminator-Main-Vent-Valve-3523000-p
Thanks!
Phillip
Here is a picture:
Thanks!
Phillip
That was a vent? Looks a lot like a hot water bleeder valve to me. Could be wrong -- have been before.Br. Jamie, osb
Close to the venting rate of this one.
https://supplyhouse.com/Ward-C-BSP-3-8-Black-Square-Head-Solid-Pipe-Plug-Steelhvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
Looks like one of those hygroscopic vents. I didn't know they made them in 3/8".
How long is the steam main, and what pipe size is it? Is this the only steam main in the building?All Steamed Up, Inc.
Consulting0 -
It was hissing out steam. Here is a picture of where I found it.
Yes, this is the only steam vent in the building.0
Not a "vent" per se, but a vacuum check. This looks like a Vapor system, probably a Dunham.
There is not supposed to be any steam in the dry (overhead) return lines of this system. Since there is, you probably have one or more bad traps somewhere.
Where are you located?All Steamed Up, Inc.
Consulting0 -
I am near Pittsburgh, Pennsylvania. I do have some bad traps that I am in the process of fixing.0
Get them fixed and see if the problem disappears.All Steamed Up, Inc.
Consulting-1 -
Good call steamhead0
The bad traps may be not only on the rads, but also in the crossover trap group.—NBC0
- 116 Geothermal