can anyone identify this main steam vent valve?
rhodebump
rhodebump Member Posts: 155
It's a 3/8 inch size. I plugged the vent for now, but I would like to order a replacement.
Here is a picture:
Would any 3/8 steam vent work such as:
https://www.supplyhouse.com/Gorton-G18-Gorton-No-1-3-8-Air-Eliminator-Main-Vent-Valve-3523000-p
Thanks!
Phillip
    Jamie Hall Member Posts: 26,709
    That was a vent? Looks a lot like a hot water bleeder valve to me. Could be wrong -- have been before.
  • hvacfreak2
    hvacfreak2 Member Posts: 500
    hvacfreak
    Mechanical Enthusiast
    Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV's
    Easyio FG20 Controller
    Steamhead Member Posts: 18,170
    Looks like one of those hygroscopic vents. I didn't know they made them in 3/8".
    How long is the steam main, and what pipe size is it? Is this the only steam main in the building?
    Consulting
  • rhodebump
    It was hissing out steam. Here is a picture of where I found it.
  • rhodebump
    Yes, this is the only steam vent in the building.
    Not a "vent" per se, but a vacuum check. This looks like a Vapor system, probably a Dunham.
    There is not supposed to be any steam in the dry (overhead) return lines of this system. Since there is, you probably have one or more bad traps somewhere.
    Where are you located?
    Consulting
  • rhodebump
    I am near Pittsburgh, Pennsylvania. I do have some bad traps that I am in the process of fixing.
    Get them fixed and see if the problem disappears.
    Consulting
    rhodebump
  • MikeJ
    MikeJ Member Posts: 103
    Good call steamhead
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,577
    The bad traps may be not only on the rads, but also in the crossover trap group.—NBC