Wiring boiler valve thermostat
Cannot figure this wiring to properly wire this to a thermostat so I don't mess it up... does anyone know the proper configuration?
  • Zman
    Zman Member Posts: 7,609
    The easiest way is to buy a zone controller like the Taco ZVC.
    Just wire it up per instructions.
    There are a few ways to tie it all together using a 24 volt transformer but the results are less than professional.
    Albert Einstein
    landeal
  • Zman
    If you are just adding a t-stat to someone else's mess, post a picture and a sketch and we can probably help you out.
    Albert Einstein
    landeal
  • HomerJSmith
    HomerJSmith Member Posts: 2,774
    The RED wires connect to the end switch (micro switch) and the TT connections on the relay or aquastat. The RED wires turn the boiler on.
    The YELLOW wires connect in this order: 24V transformer to thermostat to YELLOW wire thru (the motor) in valve (that closes the end switch) out of the valve to the transformer.
  • landeal
    landeal Member Posts: 2
    Thank you very much