Transport pipe making noices
Bosco
Bosco Member Posts: 30
edited November 2018 in Gas Heating
Why does the transport pipe making water flow noices? Each time the time is turn on
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,875
    Sounds like a low flow condition. How many pumps are on your system? Got pictures?
    ME
    CanuckerGordy
    hot_rod Member Posts: 27,104
    Could be the boiler is over sized for the loads(s) is it a zoned system? What type of heat emitters. how about a load calculation for the building.
    Copper tube boilers are a fairly low mass, low water content boiler. Without a consistent load they were prone to short cycling.
    kcopp
    EBEBRATT-Ed Member Posts: 19,920
    As mentioned above you boiler needs constant full flow when it is firing. Sounds like a flow restriction or a pump is not working
  • tommyboy5740
    tommyboy5740 Member Posts: 1
    I have the same problem with my epb 110. It started to give short term hot water and worsened to only 10 second intervals before cold water ran. I am looking for apost that may offer similar assistance.
  • Zman
    Zman Member Posts: 7,611
    @tommyboy5740
    It is probably better to start another post with all the details of your problem including pictures.
    Albert Einstein
  • Gordy
    Gordy Member Posts: 9,546
    Could be flow issue. Is this a new development, or something you just took notice of?
    Seems some flow is occurring to drop 30 degrees in 1:30 min.
    Is it warmer outside now?
  • Steve Minnich
    Steve Minnich Member Posts: 2,869
    They are suppose to be piped primary/secondary. I've yet to see one piped that way.
    Steve Minnich
  • Steve Minnich
    Or, at least, with a bypass.
    Steve Minnich
  • kjl520
    kjl520 Member Posts: 10
    If I'm not mistaken... That Laars is a copper finned boiler. Similar to a Lochinvar. You definitely have a flow issue. I've seen it many times before. These boilers have a very small volume. If you don't have constant flow through the boiler it will over heat in less than a minute. It might make some pretty weird sounds as the water boils inside the boiler. I would say your flow restriction is either from a failed pump or air lock. My money would be on a bad pump. You need a technician.
    I always thought piping a copper fin boiler with primary secondary was mandatory
    kjl520