Looking for part number for lochinvar?
kalex1114
Member Posts: 104
Hello all
I have a KHN-110 boiler and BradfordWhite SW-2-65-L indirect. Bradford white is connected via honeywell aquastat and its driving me nuts that I can't get the DHW information on the boiler. I want to get the tank sensor but I don't know what kit model I need.
Anyone have the part numbers needed?
I think replacement should be fairly simple since I beileive bradford white uses drywell for aquastat.
Thank you
Alex
Thank you
Alex
Not sure what your asking for?
Programming on boiler
Tank sensor for boiler or
Aquastat for hot water tank ?0 -
Sorry looking to replace aquastat on indirect that is wired into my boiler with tank sensor that actually reports temperatures back to the boiler
I'm looking for the part number of the tank sensor0 -
It should be in the manual0
Didn't see it in the boiler manual. I think it comes standard with lochinvar tanks. Let me see if i can find it in there0
Lochinvar supplies the sensor with the Squire series (SDT & SIT) indirect fired water heaters, so that is where the part number is listed.
The part number is #100208545, description is ' thermostat sensor'. Lochinvar shows 22 in current stock in three of their locations.0 -
It will be the same resistance. If it fits in the well, you should be good to go."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Its already used for system. So i guess i need to order another kit0
here is what i have now
Double check, you may need the sensor well also0
I measured one in stock. The actual bulb is approximately
3/8" o.d. x 1 3/4" long. It has a light wire piece attached to help it to be inserted into a dry well, two wire connection to the KHN board.0 -
I believe you are looking for TST20015 Thermostat Sensor. This sensor is not supplied with their boilers, just their indirect tanks.0
No, but any Lochinvar supplier will have, or order, or online at Boiler and Pump Supply-0
Quick question. So I found the TST20015 and about to order it. Once it arrives, I just remove the aquastat from the auqastat well on the Bradford White tank and insert the TST20015 into the same well? Am I correct on this? Then run the wires back to the boiler and attach them to the correct terminals?
Thank you0 -
Yes-0
Thank you0
Follow up. I ended up ordering TST30018 and replaced the aquastat. It was an easy swap and i just moved the 2 wires from thermostat wiring to tank sensor wiring. Only issue i discovered is that because the sensor is all the way on to bottom of the tank its slow to react and by the time it reaches to temp top of the tank is about 15-20 degrees hotter0
For another application, I will use a tekmar sensor on the larger Triangle Tube tanks because the lead wires are longer than Lochinvar's...both 10K ohms.Steve Minnich0
The well is not that deep on the tank and its all the way on the bottom. Not sure how I can improve this
Here is a picture of the tank and the sensor well. Its circled in red.
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 162 Indoor-Air Quality
- 71 Pipe Deterioration
- 393 Solar
- 55 Water Quality
- 46 Industry Classes
