Psi gauge
daveamir
Member Posts: 69
Hey good morning guys. I had a quick question when my steam boiler reaches 1psi it shuts itself off which is what it is set to do . However since the thermostat is not yet satisfied after about one minute of shutting off the boiler reaches 0 psi and the turns back on to satisfy the thermostat my question is, is this a long enough shut off time between turning back on or should there be a longer delay before the boiler turning back on or should I raise the cutoff cut in thank you
I want to say that this would not be such a big deal with natural gas ( atmospheric ) . Power burners and especially oil is so much more of a process to start and stop due to the moving parts and perhaps liquid fuel ( for oil ). Smarter burner controls have helped with this in the case of the latter however.
Either way you might be better off increasing the cut out pressure to allow for a longer " burner on " time , at 1 psi you have some room to play with.hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
-1 -
@daveamir
The solution to your problem is not a quick answer. The quick and dirty approach via raising the pressure limit is the method of last resort. Kindly answer the questions posed by nicholas bonham-carter so the true situation can be assessed. I might add one additional question to his list: Are the radiators fully heated all the way across when the boiler shuts down on pressure? If not, you have a venting issue that needs to be addressed.-1 -
Thanks for the replies I keep the ThermostT at 69 at day and 67 at night I noticing this morning as the boiler was getting from 67 to 69 that it shut off. I have a big mouth on the main and it's fully hot when the boiler shuts and I replaces all my radiator vents with gorton s and my rads are all super hot when the boiler cuts off I bet the boiler runs 30 minutes before it shuts it happenes more when the temperature goes below 30 Fahrenheit0
@daveamir sounds like it is working properly. Your boiler may be slightly oversized.
If it doesn't cut off on pressure during normal operation (not coming out of night setback) then I wouldn't be concerned. If it hits pressure occasionally coming out of night setback this would be normal0 -
Oh heavens. We've been here before. So long as this is towards the end of a longish cycle, it's not a problem. All the mechanicals which people worry about are designed for tens to hundreds of thousands of cycles; if the delay on restart is being controlled by a post purge/pre purge cycle you're fine.
Do not, repeat NOT, raise the pressure of the cutout to get a longer cycle. You will waste fuel and possibly damage traps and vents.Br. Jamie, osb
Thanks guys0