Steam boiler header
dash
Member Posts: 12
Im working on a Weil Mclain peg 45 replacing a old snowman boiler that had a counter flow system two mains running left and right side of the house and each had a drip . I was hoping that someone could give me a better piping diagram then the manual it didn't seem to show a drop header the way I thought it would be piped. I'm not sure where to pipe the drips for the mains should these dump in to the wet leg after the Hartford loop?
Thanks John
Thanks John
https://us.v-cdn.net/5021738/uploads/editor/35/qptw1srfp83h.jpg
This looks the same as the one in the Peerless manual.—NBC0 -
Follow the above posted by @nicholas bonham-carter and you will be fine0
The manual doesn't show where the drips from the mains tie in0
As I recall, there's no real need for a Hartford loop since there is no return piping. Running the drips down into the return tapping should do it.
I found this would this be an approved method of piping0
Here's the one:
New England SteamWorks
newenglandsteamworks.com0 -
I ran mine like this on the last counterflow job, the reason I dripped in that location is because that was the lowest point.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
Thanks everyone for the feedback
I have one more question do I have to have a double riser off the boiler or can I stay with one 2 1/2 and 2 1/2 header with two -2” tees for supply’s and then to a
1 1/2 equalizer line0 -
depends on the steam velocity out of your boiler. Most here will use both even on small boilers0
What does the manufacturer say.0
The manual shows one riser at 2 1/2" and a
2 1/2" header0 -
Nothing succeeds like excess, as they say. Use both risers.
Be happy.New England SteamWorks
Dave my system is Similar to yours other than having two mains running say east and west sides of house
I see you piped up over the main and then back down in to it would this be a issue or good practice
Thanks John0