1107-1 boiler control
Shadow19
Shadow19 Member Posts: 1
all the lights on the weil mclain 1107-1 integrated boiler control are out. no blinking nothing i dont have my meter so I cant check for power. also no pilot only thing working are the circulators. its got to be the control?
    HVACNUT Member Posts: 7,411
    Get a meter and post some pics.
  • Fred
    Fred Member Posts: 8,542
    May be a stupid question but is the boiler/controls on a seperate breaker from the circulators? Is that control fused?
  • Tim McElwain
    Tim McElwain Member Posts: 4,660
    I will get back to you tomorrow as I have literature on that control but it is at my training center.
  • lchmb
    lchmb Member Posts: 2,997
    is this a cg boiler? Single circ wired to the boiler or multiple wired to a circ control? Hard to trouble shoot without a meter..
  • Tim McElwain
    Go to "R" to "BR" do you have 24 volts? If so then your 120 volts and your transformer are okay.
  • Tim McElwain
    I guess we are not going to hear from shadow19 any more???
    I think he's still looking for his meter.