Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
1107-1 boiler control
Shadow19
Member Posts: 1
in Gas Heating
all the lights on the weil mclain 1107-1 integrated boiler control are out. no blinking nothing i dont have my meter so I cant check for power. also no pilot only thing working are the circulators. its got to be the control?
0
Comments
-
Get a meter and post some pics.0
-
May be a stupid question but is the boiler/controls on a seperate breaker from the circulators? Is that control fused?0
-
I will get back to you tomorrow as I have literature on that control but it is at my training center.0
-
is this a cg boiler? Single circ wired to the boiler or multiple wired to a circ control? Hard to trouble shoot without a meter..0
-
Go to "R" to "BR" do you have 24 volts? If so then your 120 volts and your transformer are okay.0
-
I guess we are not going to hear from shadow19 any more???0
-
> @Tim McElwain said:
> I guess we are not going to hear from shadow19 any more???
I think he's still looking for his meter.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements