1107-1 boiler control
Shadow19
Member Posts: 1
in Gas Heating
all the lights on the weil mclain 1107-1 integrated boiler control are out. no blinking nothing i dont have my meter so I cant check for power. also no pilot only thing working are the circulators. its got to be the control?
0
Comments
-
Get a meter and post some pics.0
-
May be a stupid question but is the boiler/controls on a seperate breaker from the circulators? Is that control fused?0
-
I will get back to you tomorrow as I have literature on that control but it is at my training center.0
-
is this a cg boiler? Single circ wired to the boiler or multiple wired to a circ control? Hard to trouble shoot without a meter..0
-
Go to "R" to "BR" do you have 24 volts? If so then your 120 volts and your transformer are okay.0
-
I guess we are not going to hear from shadow19 any more???0
-
> @Tim McElwain said:
> I guess we are not going to hear from shadow19 any more???
I think he's still looking for his meter.0