Nest contactors running radiant UFRH
Danroonie
Danroonie Member Posts: 8
edited November 2017 in Thermostats and Controls
I am working on heating a 3 room cabin in PA. There is 200 amp service - so plenty of juice to heat it.
The house will only be occupied 1/2 the winter - and internet is available, so an app can tell the 2 nests to call for heat so the homeowner can turn up the heat on the way to the cabin. Each zone has UFH (under floor electric heat) and a less desirable - but fast acting in-wall electric heater (aux) 240V 20 amp. The nest has an aux setting. I got feedback from this forum recommending the contactors but I wanted to get final feedback on the setup. See diagram
    HVACNUT Member Posts: 7,381
    I would change the transformer to a 50va max and fuse it. Do you know the current draw from the two relay coils, and if the Nest can handle it?
  • ratio
    ratio Member Posts: 4,216
    We covered that in another thread.
  • Danroonie
    Per ratio's earlier suggestion - the transformer is serving 2 zones- so essentially 50va is available minimum per zone off the 100 va transformer - I've updated the diagram since it was vague. Where would you put a fuse? What would it protect? Thanks!
  • BobC
    BobC Member Posts: 5,554
    i would fuse the output of the transformer, start with a 2a slow blow (might have to go up to 3a) so it doesn't pop on inrush current.
    Bob
    3PSI gauge
  • Danroonie
    MT0100C has a built-in holder- So 3amp slow blow like this? From amazon I looked at the tech sheet on the seimens site- but it didn't say if 5mm x 20mm is the right size. Tried to get it unsuccessfully at supply Cooper Electric and NAPA auto.
    Thanks Bob and Ratio