I am working on heating a 3 room cabin in PA. There is 200 amp service - so plenty of juice to heat it.
The house will only be occupied 1/2 the winter - and internet is available, so an app can tell the 2 nests to call for heat so the homeowner can turn up the heat on the way to the cabin. Each zone has UFH (under floor electric heat) and a less desirable - but fast acting in-wall electric heater (aux) 240V 20 amp. The nest has an aux setting. I got feedback from this forum recommending the contactors but I wanted to get final feedback on the setup. See diagram
The house will only be occupied 1/2 the winter - and internet is available, so an app can tell the 2 nests to call for heat so the homeowner can turn up the heat on the way to the cabin. Each zone has UFH (under floor electric heat) and a less desirable - but fast acting in-wall electric heater (aux) 240V 20 amp. The nest has an aux setting. I got feedback from this forum recommending the contactors but I wanted to get final feedback on the setup. See diagram
0
Comments
-
I would change the transformer to a 50va max and fuse it. Do you know the current draw from the two relay coils, and if the Nest can handle it?0
-
We covered that in another thread.0
-
Per ratio's earlier suggestion - the transformer is serving 2 zones- so essentially 50va is available minimum per zone off the 100 va transformer - I've updated the diagram since it was vague. Where would you put a fuse? What would it protect? Thanks!HVACNUT said:I would change the transformer to a 50va max and fuse it. Do you know the current draw from the two relay coils, and if the Nest can handle it?
0 -
i would fuse the output of the transformer, start with a 2a slow blow (might have to go up to 3a) so it doesn't pop on inrush current.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
MT0100C has a built-in holder- So 3amp slow blow like this? From amazon I looked at the tech sheet on the seimens site- but it didn't say if 5mm x 20mm is the right size. Tried to get it unsuccessfully at supply Cooper Electric and NAPA auto.BobC said:might have to go up to 3a) so it doesn't pop on inrush current.
Thanks Bob and Ratio0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements