Reason for flame to roll out
Hi all,
Had a roll out switch go bad checked flue and damper and chimmeny but nothing blocking very dirty so I thought maybe the burner or heat exchanger need cleaning is that possibly the Reason? Any suggestions or answers would be greatly appreciated... Stay warm
  • danitheplumber
    danitheplumber Member Posts: 98
    Dunkirk boiler and chimney is completely black on the top outside
  • j a_2
    j a_2 Member Posts: 1,804
    What ever you do find the cause....blocked passage ways between sections...lack of or make up air issue...gots to find the cause...ya got a draft hood that is a match for the boiler...? Dampener is fully opening correct? Almost has to be, cause it won’t start UNLESS, someone was a tinkering in there....any way good luck...
  • danitheplumber
    Damper is set in open position always. Non of the flue is blocked. Exchanger dirty and chimney dirty burnwr probably dirty but just wondering if that would cause flame to roll out.
    HVACNUT Member Posts: 7,177
    Clean the heat exchanger, burners and orifices. Check lockup and manifold pressures. Do a combustion analysis.
    Standing pilot or spark?
    danitheplumber
  • danitheplumber
    Standing customer doesn't want to pay for cleaning
  • KC_Jones
    KC_Jones Member Posts: 5,895
    Then the customer obviously doesn't care if their equipment works properly.
    They will end up jumping the safety out and then you will read about them on the news.
    I would seriously tell them this so they understand they aren't doing it correctly.
    The other alternative is to walk away and let hackasaurus rex take care of them since that is apparently what they want.
    If it's black it needs cleaned and the burner adjusted and set up properly.
    2014 Weil Mclain EG-40
    danitheplumberJohnNY
    EBEBRATT-Ed Member Posts: 19,333
    Then, fire the customer!! What @KC_Jones said is good (and the only) advise you should listen too. This could be dangerous and you and your company doesn't need the liability.
    Some companies and probably the local gas utility would shut the gas off and red tag the unit until it is repaired.
    You don't have to work on this pc of crap. You need to make the customer understand with a little tough love and....get it in writing on your service slip and get it signed
  • ratio
    ratio Member Posts: 4,170
    I've said it before, I think:
    Not all customers need to be our customers.
    Tell them, honestly and without malice, that what they're electing to do is so dangerous that you are not going to be able to perform any more work for them, for fear of liability; & then WALK AWAY.
    That may be enough to convince them to perform the proper maintenance, but in all honesty unless they were family or something I wouldn't go back.
    danitheplumber
  • GW
    GW Member Posts: 5,133
    Toss the customer back in the water
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    BobC
    @ratio said: "unless they were family or something I wouldn't go back."
    In my experience, if it's family or friends run away...............Faster
    They always want a deal lol
    j a_2HVACNUT
  • Tim McElwain
    Tim McElwain Member Posts: 4,657
    Shut the equipment off and make it inoperative. Then contact local utility and the fire department and advise of the unsafe operation and how you left it. Then send the customer a registered letter to protect your self from any come back.
    BobCHVACNUT