Wiring Honeywell HZ311 from a Trol-A-Temp Mastertrol Mark VII

My question is if I am replacing my entire control panel I have today with the Honeywell HZ311, or do they have to work together. I've provided some pictures as well for my existing set-up. I'm also confused as to my current set-up going into the HZ311.
My current setup just has red/white wires connecting into my mastertrol and then the color wires going into the selector switch marked 11 through 19. Not sure how that connects into the HZ311.
I should also mention my system has a master switch that is changed seasonal from Heat to Cool for the switch from my system providing heat to AC.
Thanks ahead of time for any help.



Comments
-
Take a look at this thread.0
-
Thanks ratio. I looked over that thread and it made some points, but it wasn't clear on the exact wiring from what I understood. My wiring seems to be different from what was discussed in that thread. For instance, that I have red & white wiring into my different Y,G,R,W,A section as well as what to do with the wires connecting selector switch 11 - 19. Also wasn't clear if this was replacing the troll master completely or working with it. Sorry, definitely new to all of this.0
-
Ok. There's three main parts to these systems.
- Thermostats
- It appears that you have enough conductors to use whatever thermostat you wish—but I am not sure if the current stats will be sufficient
- Dampers
- The Trol-A-Temp actuators can be used with the Honeywell panel
- The furnace/AC control
- If it heats & cools now, it will do it when we're done
As an added benefit, the TrueZONE panel will do automatic changeover, so you won't have to switch the system from heat to cool any more.
I'm having trouble finding a schematic for that model of controller. Perhaps the manual is laying around there? A few pics of the wiring diagrams would help immensely.

The thermostats will be quick & easy, ahthough you might have to replace that 3 conductor that's landed on zone 3; and the zone dampers will be straightforward as well, but the furnace wiring itself is going to take some puzzling out.


The zone actuators should be rewired as noted here.
The thermostats should be replaced with whatever you chose to use, wired like to like on the zone terminal strip. You'll need to replace the 3 conductor that's on zone 3, you'll need a minimum of 4, 5 if you don't want batteries. An option you might want to consider is RedLINK wireless, again details are in that other thread. (An internet gateway is available that will give you smartphone access)
That should be everything, but note that there is some rework at the damper actuators themselves that might need to happen. There are extra wires going to the master stat, we won't need those any more, as the TrueZONE does automatic changeover. You are planning on replacing all the thermostats, right? I'd suggest something that provides an "auto" mode, so you don't have to change the mode of the stats every season.
This shows how to wire the damper actuators to operate on a 3 wire system. Basically add a jumper at the actuator. I'm assuming that you have the MST actuators as illustrated in that PDF.

Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 110 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 106 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 978 Plumbing
- 6.3K Radiant Heating
- 387 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements