gas conversion burner flue
Dan467
Dan467 Member Posts: 11
how do i size chimney liner size , oil boiler 7 inch water heater 4 inch btus or sq inches?
  • Tim McElwain
    Tim McElwain Member Posts: 4,657
    What is the input to both appliances?
  • Dan467
    40k and 120k
  • captainco
    captainco Member Posts: 840
    Square inches is always safer than btus Btus never allow for excess air or dilution air.
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,422
    btus is only approved method by NFPA 51, 52,
    cell # 413-841-6726
  • captainco
    NFPA did not approve the btus method, they approved the computer program that created the marginal venting tables. You must go back to the original development of the GAMA Venting Tables in 1988-89. If you read what they say, you might see that area would be safer.
  • Tim McElwain
    Jim is correct I however always like to check it both ways. I guess old dogs never change their ways unless they find out that the way they have always done it is not necessarily the correct way. I agree using are is the best way. Many of the installation manuals for conversion burners would give you size based on BTU.