Galaxy cast iron boiler
Does a galaxy cast iron boiler ( model GG125HXP REQUIRE A CIRC. PUMP ?.
  • Ironman
    Ironman Member Posts: 7,842
    EVERY boiler in a forced flow hot water system requires a circ.
    If it's an old gravity flow system with a boiler designed for gravity flow, that's a different animal.
    Bob Boan
  • Danny Scully
    Danny Scully Member Posts: 1,465
    If you meant does it come packaged with one, I believe it comes with a TACO 007, no flow check.
  • jumper
    jumper Member Posts: 2,495
    I think the question is does it require a circ pump?
    A gravity system today would be interesting.
    Steamhead Member Posts: 18,183
    It does. There is too much resistance inside the boiler to allow gravity flow.
    Consulting
  • Razor
    Razor Member Posts: 4
    Problem is ,the system was working fine , then I added a line of slant fin , 8' lg. and there is no heat getting to this !
  • Ironman
    Most likely, it's air bound. That's assuming it's piped correctly. If it's a monoflo system, it can be extremely difficult to get all of the air out.
    Bob Boan
  • Razor
    Should there be a circ. PUMP on this?
  • Razor
    On this system .
  • KC_Jones
    KC_Jones Member Posts: 5,902
    You are going to need to post a lot more information about your system.
    Is the house radiators or baseboard originally?
    Does it have a pump now?
    Pictures of what you have and what you added would help a lot.
    2014 Weil Mclain EG-40
    IronmanNew England SteamWorks