Burnham megasteam boiler
t hardy
t hardy Member Posts: 29
I just installed a Burnham megasteam boiler - over time it starts to flood - the water in the sight glass slowly gets higher and higher. The water is clean. Any suggestions appreciated.
Thanks much!!
  • lchmb
    lchmb Member Posts: 2,997
    do you have an auto feeder? Do you have a bypass with a gate valve? Is it piped properly? How was the old boiler piped? More information is required...
  • BobC
    BobC Member Posts: 5,538
    One way to check if a valve is leaking by is to feel the pipe a foot above and below the valve.
    if both are about room temperature (same temp as other metal objects nearby)you are usually fine.
    If both are cold you have water flowing through that valve.
    if both are cool you have water seeping past the valve. Note if the seep is very small this takes good judgement and experience to discern.
    Bob
    3PSI gauge
  • t hardy
    I have a needle valve on the feed line - set way down.
  • KC_Jones
    KC_Jones Member Posts: 5,902
    Is there another valve after the needle valve? The feed should be completely off unless either you manually add water or an automatic feeder adds water.
    By your description it gives the impression the water is on all the time.
    2014 Weil Mclain EG-40
  • Ironman
    Ironman Member Posts: 7,844
    What's a "needle" valve? Do you mean a saddle tap valve?
    As KC said, water should be shut off once the boiler is full, not just "set way down".
    You may also have a clogged return line. If so, condensate would be slow to return to the boiler causing it to appear low and more make up to be added. Then, as the condensate slowly seeped back into the boiler, the water level would rise too high.
    Please post some pics of the boiler and it's near piping so that we can see the total picture of what's there.
    Bob Boan
  • Dave0176
    Dave0176 Member Posts: 1,178
    One question does the boiler have a domestic hot water coil in it?
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • t hardy
    auto feed with a needle valve to restrict flow when more water is called for -
    no hot water coil -
    near boiler piping kit is from Burnham -
    all return lines replaced and increased in size
  • Danny Scully
    Danny Scully Member Posts: 1,465
    Please post pics...and where did you get this needle valve idea from?
  • t hardy
    probably fw webb
  • Fred
    Fred Member Posts: 8,542
    Has this new boiler been skimmed, several times to remove all the oils from the surface of the boiler water? If not, the water line can be so unstable when the boiler runs that the water line drops enough that the LWCO calls for water when it really isn't needed and the fact that you have that needle valve on there to restrict the flow of water probably explains why the water level just creeps for now, since we are in the shoulder season. When it gets colder and the boiler runs for longer periods, there will likely be more calls for water and the water level will rise quicker. Make sure the skimming is done if the water bounces more than a half to 3/4 of an inch or if there are droplets of water in the top half of the sight glass or oils setting on top of the water in the sight glass.