Only 1 out of 7 baseboard have heat coming out
chris_j11
Member Posts: 1
House Heating system: Mini Gas Low Pressure Boiler
I have 4 Thermostats in the house (1-Master Bedr, 1-Kids room, 1-computer room, 1-living room)
All 3 rooms are generating heat exept in the living room.
The living room have 7 baseboard and only 1 of them is generating heat
what would caused the other baseboard to not generate any heat?
I check the crawl in, and I can visibly see all the pipes running to each baseboard and i don't see any leak and none of them are warm/hat to touch
This really isn't radiant heating -- but let that go. Is there any way to check for air in the baseboards which aren't operating? That's the most likely problem. You should also check that there is adequate pressure in the system as a whole -- 15 psi is kind of a minimum.
Then if there is, you may have to bleed air out of those baseboards which aren't operating.Br. Jamie, osb
Besides air you could have a bad circulator, or malfunctioning zone valve and you only feel heat because of some gravity flow.
With 4 zones, I would bring out a pro to properly purge the system, and check the equipment.There was an error rendering this rich post.
post a picture of the boiler and near boiler piping..step back and get a full view..0
