Why cant I get these oil burners to fire when I bring 120v directly to primary Control?
Joseph_4
Joseph_4 Member Posts: 320
Hi
Can someone tell me why I cant get a few Beckett AfG burners with Honeywell 7184B Primary control combination to fire when I bring 120 Volts directly to the white and blk.( Iam trying to change the blast tube and end cone using the same burner chassis for a different boiler) When I do this the steady green light comes on which means burner on while nothing is happening. I have tt jumped out. When I do this with Riello Burners and carlin Burners they fire right up. What am I missing? All the burners were working when I pulled them off boilers to change them to gas burners
I have attached some pics
Thanks
Joe
HHI Services
    Steamhead Member Posts: 18,525
    If the green light is lit when you power up the control, the cad call is detecting light. The control is programmed not to start the burner if it sees light.
    Try disconnecting one of the yellow wires at the control and see if that helps. Of course, with the wire disconnected, the control will lock out after the trial for ignition.
    Consulting
    New England SteamWorksIronmanGrallert
  • newagedawn
    newagedawn Member Posts: 585
    i agree with steamhead or that primary control is bad, also that control needs power to it to function, cant jump them like the grey box ones
    "The bitter taste of a poor install lasts far longer than the JOY of the lowest price"
  • dennis53
    dennis53 Member Posts: 68
    I can't tell from the picture but did you energize the limit wire as well?
    Dennis
    Grallert
  • Joseph_4
    I thought that might be problem and pulled out cad cell and put finger over it while applying power and nothing changed.. i believe when bring power directly to burner you are bypassing limit.. its no different then bi and b2 from l8124c TAR sending the 2 wires to power burner
  • STEVEusaPA
    edited October 2017
    Seems like you are trying to bench fire this burner. Covering up the cad cell eye with your finger is not the same as removing one yellow wire. Remove wire, reset control. After prepurge and you hear the oil valve open, reconnect wire.
    You could disconnect the motor and see if you have 120 coming from the motor terminal.
    Keep in mind, that this is dangerous, and if the cad cell is seeing light with the unit not running, then it stands to reason it will see light if the flame drops off and continue pumping oil. So don't leave this unattended during your experiment.
    Ironman
  • Joseph_4
    Thanks for all the responses.. . Did what steve told me. All Fired up
    Joe
    HVACNUT