P/S Piping 1971 Utica model PGB100 to unscrew or not to unscrew ..that is the question
Options
HydroNiCK
Member Posts: 186
I have a feeling that I'm not going to be able to unscrew this nipple even if i wanted to..what say yous..? I want to p/s pump my system. My calculations call for 1"pipe However as you can see in the pics. The return tapping is 1-1/2" reduced to 3/4 and the supply is 1-1/2" with 1-1/4" reducer currently reduced to 3/4. Can I leave the tappings alone and use 1" to 1.5" reducers at the nipples? Will it be too much of a problem with my flow?






0
Comments
-
You need 1" IPS to get the correct flow for that boiler
But If the nipples coming out of the boiler are 3/4" and are only a few inches long (say 6") and you can increase the pipe size to 1" right away you will be ok. You need to move 8 gpm0 -
-
Why would you want to re-pipe a 46 year old boiler? If it works, leave it alone. If you want better efficiency, then it's time for a new one. I can't see where p/s is gonna be any benefit.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements