Airing our heating system
eclass
Member Posts: 8
in Oil Heating
Hi everyone, I'm just looking for a bit of help or suggestions.
yesterday, I had a new baseboard installed. the person who installed it didn't shut off any valves or anything.
I read that anytime you replace a hot water baseboard system the lines would need to be aired out.
I'm trying to figure out which levels I have to shut down. Also, from what I read around I need to install a hose and let the water/air out from the system. I believe the hose needs to be attached right above the circulation pump. (see photos)
Any information would you can provide would be great!
Thank You.
Thank You.
I forgot to mention that I did run the system for a bit but I stared to hear a humming sound coming from the circulation pump, the pump also become pretty hot too.0
With the boiler off, close the red handle valve above the circulator. Attach a hose to the boiler drain just above. Put the other end of the hose outside or in a drain. Open the boiler drain until a steady stream of clear water comes out of the house, or at least for 5 minutes.
If you loose pressure while purging, then the manual lever on the boiler fill valve needs to be opened. BE CAREFUL not to let the boiler pressure get above 25 psi. At 30 psi, the relief valve will open and dump water.
Once the air is purged, close the manual fill FIRST, then close the boiler drain after the pressure has dropped back to about 12 - 15 psi. Then open the red handle valve and start the boiler.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
IronMan Thank you!!!!!!0
I will look that this tonight0
- 87K THE MAIN WALL
- 58 Biomass
- 113 Chimneys & Flues
- 109 Geothermal
- 161 Indoor-Air Quality
- 995 Plumbing
- 391 Solar
- 55 Water Quality
