Relief valve installation - Go or NO GO
Dale_3
Member Posts: 58
All - We have had numerous conversations as of late regarding relief valve installations and I'm getting put in the "he's crazy" corner again. In my opinion "and I believe the code says" this is not installed correctly.
What are your thoughts? "And code references"
Not a code expert -- but I don't like it. When that puppy opens you are going to have a spray all over the place. I'd rather see a pipe from the outlet to down near the floor...Br. Jamie, osb
I think he means the orientation. I prefer pressure only relief valves to discharge horizontally, with a drip leg as @Jamie Hall suggests.1
#7
As @bob shows in his post the valve must be mounted straight up with the stem in the vertical position.
Boiler inspectors in MA are insisting on this for both steam & water, it's ASME Code even if it's not on a boiler
Also a blow off pipe piped to a safe location with the blow off pipe supported to allow no strain on the valve0 -
All - Thanks for the comments. The vertical position was one of the issues. I should have pointed out that this was a new "yet to be turned on" installation and the discharge piping was not done yet. One other issue "I believe" is the connection point should be on top of the pipe. Anyone have any thoughts on that?0
On top would certainly keep less crap from blowing/washing into it.0
Does anyone have access to the Boiler and Pressure Vessel Code? (at least a snippet about this specific subject) My Google searches have not turned up much and I don't have the $ to buy it.
Thanks again - Dale0 -
@EBEBRATT-Ed - Thank you for the additional information.0
If steam is in the shell, is there a vacuum breaker on the shell itself?0
- 117 Geothermal