One expansion tank per system
Is the wood boiler pressurized?Bob Boan
One way or another, you will need extra expansion tank volume to handle the additional volume of heated water in the new boiler, buffer tank, and boiler.0
Is there a such thing as "too much expansion tank" ?
A piping diagram would be helpful. If the entire system is pressurized and all shares the same water, the you (he) is best served by one large expansion tank. Arranged to be pumped away from. There is no such thing as too much expansion. A buffer and boiler will likely add 100+ gallons to the system fluid. His existing tank is likely an EX30 or EX60, not worth keeping. Pump away from wherever you locate the expansion tank connection! You will save a world of headache, also I'd recommend a good microbubble air separator at the wood boiler supply. I head reoccurring air issues which were completely eliminated buy a spirovent.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
WW you are correct 1 per system.
Pumping away from the circ in the primary loop.
Make it a big one.
You can have more than one, but they all have to connect to the piping system at a single point. If you don't do this, the point of no pressure change will appear somewhere in the system between the multiple tanks, which will cause water to move in and out of the tanks. Not a good idea.Retired and loving it.1
The way that I learned it, yes. An oversized expansion tank will absorb water volume until the water temperature it takes to hit 30 psi (or whatever relief valve setpoint is on the system) can be approaching 300° or more. If a relief valve opens at very high water temperatures, it can be dangerous for property and people that are in the area, as the water will flash to steam pretty violently.ChrisJ said:Is there a such thing as "too much expansion tank" ?
If the tank is precharged to the proper pressure, why wouldn't it work like any other in the same system, oversized or not?
As far as expansion, it would work fine. A properly sized tank wouldn't allow the relief valve to open unless the temperature limit failed, then the rising temperature would build pressure until the relief valve opens. The tank size determines how far it rises before opening the relief valve.
30 PSIG is 30 PSIG, it doesn't matter how much water is behind it.Noel said:As far as expansion, it would work fine. A properly sized tank wouldn't allow the relief valve to open unless the temperature limit failed, then the rising temperature would build pressure until the relief valve opens. The tank size determines how far it rises before opening the relief valve.
That's the part I'm not getting. Would the oversized tank hold more water? Yes.But I can't see it mattering, especially considering the huge size of the tanks from the days before bladder tanks.
That's the part I'm confused by.
30 psi at 240° is safer than 30 psi at 340°. The question isn't what the pressure is when it opens, it is what the water temp is when it hits 30 psi and opens.
Its a tough concept to explain, and most guys training people don't even bother trying.0 -
The bigger tank will accept more water than the smaller one. Therefore, the water will have to expand more to fill the larger tank than the smaller tank before the relief pressure is reached —this means more heat will be accepted by the water before the relief valve will be forced open.0
Yes, but the temperature will remain the same regardless of btu's taken in. Because as you said, there's more water.ratio said:The bigger tank will accept more water than the smaller one. Therefore, the water will have to expand more to fill the larger tank than the smaller tank before the relief pressure is reached —this means more heat will be accepted by the water before the relief valve will be forced open.
How much more water will a larger tank accept, a gallon? Do guys limit piping runs for the same reason?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Noel's chart assumes the limit is busted .
In order for 340F degree water to exist, the system would need 106 PSIG in it.Noel said:
The highest you can go with 30 PSIG is around 273F before boiling.
30 PSIG water at 340F does not and can not exist regardless of expansion tank size.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Um, no. Maybe ask Amtrol about that. That's where I got it from.0
With all due respect, I don't need to as Amtrol about that, that's how it works.Noel said:Um, no. Maybe ask Amtrol about that. That's where I got it from.
You cannot exceed the boiling point of any liquid at any given pressure. Even if Amtrol say's you can.
@bob iscorrect, only if the limit's busted. that's why 2 limits (1 regular and 1 man reset is best)
Other than that a larger expansion tank has no dettrimental effect cept for cost1
- 62 Biomass